    Question Help with Carrel PCO5/HMI



    hello,
    our plant is stopped since 2 days because of chiller HMI break down.
    we have contacted the manufacturer and it will take more than 2 weeks to send the new HMI and they refused to send the program to download it for a new clear HMI
    is there any way to run the chiller without the HMI?
    the PCO got alarms and we need to reset them before switching the compressor switch ON
    thanks in advance for your help



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Help with Carrel PCO5/HMI

    There is possible to control PCO through network interface if it is programed in it.
    Last edited by nike123; 14-12-2020 at 09:39 PM.

  3. #3
    Join Date
    Dec 2020
    Location
    Paraguay
    Posts
    3
    Rep Power
    0

    Re: Help with Carrel PCO5/HMI

    If you have pCOWEB card you can interface directly using web interface.

  4. #4
    Join Date
    Mar 2020
    Location
    Italy
    Age
    37
    Posts
    13
    Rep Power
    0

    Re: Help with Carrel PCO5/HMI

    The PCO HMI has no software on it. Get another HMI and test it. Maybe you need to set the address of the HMI(Press and hold up down and enter then plug in the power source)