Thread: Carel alarm
    May 2020
    belgium
    15
    Carel alarm
    Hello,
    Carel for chiller type μC2SE: gives alarm ELS, low voltage. Voltage is correct.
    Step 1 is not activated, but step 2-3-4 is activated.
    Somebody an idea?
    Greetings Fernando
    Somerset
    69
    4,697
    Re: Carel alarm
    Hi.
    Out of interest what chiller is this fitted to?
    Only I have seen this fault arise when the supply to the machine is interrupted.
    Basically the fault shows when the chiller is powered back up.
    If i remember correctly it clears itself over time.
    If the above applies then just leave the chiller and the fault should clear.
    May 2020
    belgium
    15
    Re: Carel alarm
    Hi.
    Hello
    The chiller type i dont know. I did not see the nameplate.
    It is a R290 chiller.
    The alarm stays, not goes away.
    Greetings
    Oct 2001
    Nottingham UK
    5,668
    Re: Carel alarm
    I've had a similar incoming voltage alarm on a Daikin chiller.
    The alarm was very random and took ages to find. Turned out to be the signal wire from the slide valve picking up interference. rerouted the signal wire and all good since.
    May 2020
    belgium
    15
    Re: Carel alarm
    Everything we tried gives no results, sill same alarm.
    I am going to change the Carel.
    Greetings
    Oct 2016
    Serbia
    110
    8
    Re: Carel alarm
    Change controller