    York chiller heating will not start



    Hello
    I have a York YVAG012RSE30 new.
    There is water on the system, de air is out the system.
    When i plug it in, 230V, i get EE on the display.
    A timer on the print count 160 seconds, after that nothing happens.
    EE stays.
    Somebody familiar with this?
    Greetings Fernando.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: York chiller heating will not start

    EE error code is for a water level fault.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2020
    Location
    belgium
    Posts
    15
    Rep Power
    0

    Re: York chiller heating will not start

    I just have found the problem.
    There are dip switch inside the remote. 4-5-6 has to be ON.
    Nothing is written on the manuel. The manual from York is incomplete.

  4. #4
    Join Date
    May 2020
    Location
    belgium
    Posts
    15
    Rep Power
    0

    Re: York chiller heating will not start

    Problem was the dip switch from the remote controlle.
    Some has to be in the ON position, depends from what sort of installation.