    Return gas temperature



    Hi friends,
    What is effect of return gas temperature on compressor capacity ?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Return gas temperature

    Any incresae in temperature added to the suction gas after the evaporator will reduce system refrigerating capacity and increase the power required to run the compressor. The excess heat absorbed into the suction gas will also have to be rejected in the condenser before saturation can take place.

    3K of suction gas superheat is considered 'useful' superheat as this ensures that no liquid refirgerant returns to the compressor, anything above 3K in considered 'non-useful' superheat.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: Return gas temperature

    https://www.achrnews.com/articles/14...essor-capacity

    This seems to explain things pretty well

  4. #4
    Join Date
    Jun 2017
    Location
    Norway
    Posts
    32
    Rep Power
    0

    Re: Return gas temperature

    Also having to low of an superheat can cause the oil in hermetic compressors to be washed/mixed with to much refrigerant and decrease its lubricating properties.