    2 Compressor in 1 system



    Hi,
    I am making a chiller for injection molding and plan to install 2 compressor in a system being 1 primary and 1 secondary.
    Primary would be running at all times while secondary would be used when temperature from primary could not be attained and need extra power for extra load.

    I am confused with 2 question and need expert advice.

    1) If I install 2 compressors than should I place NRV on both compressors on both suction and discharge side?

    2) one of local compressor was advising me to drill a liner horizontal pipe between 2 compressor for compressor oil of both compressors to be equal at all times, according to him if I don't do this then oil on compressor will not be balanced.

    Diagram below:
    2ndcompressor.jpg

    Regards
    Salman
    Attached Images Attached Images



  2. #2
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: 2 Compressor in 1 system

    Hi
    Would appreciate follow up

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: 2 Compressor in 1 system

    Hi, skhan855

    Quote Originally Posted by skhan855 View Post
    Hi
    Would appreciate follow up
    after maybe only 24 hours without reply to your request
    this is not necessary ...
    we all are here voluntary

    (our daily bread we have doing our normal jobs)

    someone will give you some advice when get a
    free time for it ....

    Maybe I sound rude, but we have to respect everyone
    who is spending own free time here to help someone ...
    so, no need to push .....

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: 2 Compressor in 1 system

    Ofcourse, thats why I asked initially asked advice in a respected manner. I really appreciate contribution of members on this forum as it helped me earlier in lot of cases.

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: 2 Compressor in 1 system

    Quote Originally Posted by skhan855 View Post
    Hi,
    I am making a chiller for injection molding and plan to install 2 compressor in a system being 1 primary and 1 secondary.
    Primary would be running at all times while secondary would be used when temperature from primary could not be attained and need extra power for extra load.

    I am confused with 2 question and need expert advice.

    1) If I install 2 compressors than should I place NRV on both compressors on both suction and discharge side?

    2) one of local compressor was advising me to drill a liner horizontal pipe between 2 compressor for compressor oil of both compressors to be equal at all times, according to him if I don't do this then oil on compressor will not be balanced.

    Diagram below:
    2ndcompressor.jpg

    Regards
    Salman
    Salman,
    Yes advice is correct, but only require check valve in compressor discharge.
    Pipe so oil cannot accumulate in its discharge pipework if off for extended periods.

    Yes also need to balance/equalise compressor sumps, usually compressor has to be designed for this when purchased.

    https://assets.danfoss.com/documents...0286438497.pdf

  6. #6
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: 2 Compressor in 1 system

    Thanks Ranger1, this means 1 NRV to each Compressor on discharge side and no NRV on sunction side?

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: 2 Compressor in 1 system

    Quote Originally Posted by skhan855 View Post
    Thanks Ranger1, this means 1 NRV to each Compressor on discharge side and no NRV on sunction side?
    Yes, I think so, as stops condensed liquid on compressor head.
    Another Danfoss paper, maybe a bit better.

    https://assets.danfoss.com/documents...8786422181.pdf

  8. #8
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: 2 Compressor in 1 system

    Quote Originally Posted by RANGER1 View Post
    Yes, I think so, as stops condensed liquid on compressor head.
    Another Danfoss paper, maybe a bit better.

    https://assets.danfoss.com/documents...8786422181.pdf
    Thanks, it really helps

  9. #9
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: 2 Compressor in 1 system

    Quote Originally Posted by RANGER1 View Post
    Yes, I think so, as stops condensed liquid on compressor head.
    Another Danfoss paper, maybe a bit better.

    https://assets.danfoss.com/documents...8786422181.pdf
    Hi
    Yes this a 1 reason
    Another important reason
    if on of the discharge valve plate is brocked.
    Provent gas goes to suction side in rack system.

    In rack system also blanceing of oil should have good attention with oil filter and insulate valves.
    Last edited by mbc; 16-10-2020 at 05:15 PM.

  10. #10
    Join Date
    Apr 2020
    Location
    New Zealand
    Posts
    10
    Rep Power
    0

    Re: 2 Compressor in 1 system

    Oil balance line required, discharge check valves (nrv) recommended.
    Also, oil balance lines require careful installation as separate compressors can twist and break connections.
    Scrolls are especially bad, but solid mounting eliminates this issue. (Noise not too bad with scrolls) recips, just make sure you have a couple 90 elbows between comps.
    Avoid flare connections where possible.
    How do you intend to control the comps?
    If using lp switch, I suggest a delay timer on 2nd comp. Digital control, set a delay.
    Good luck and have fun..

  11. #11
    Join Date
    Oct 2020
    Location
    india
    Age
    39
    Posts
    13
    Rep Power
    0

    Re: 2 Compressor in 1 system

    Hi i would say your thinking is good . go for this

  12. #12
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: 2 Compressor in 1 system

    Quote Originally Posted by CoolKiwi View Post
    Oil balance line required, discharge check valves (nrv) recommended.
    For discharge valve better use nrvh - with stronger spring.
    For oil equalization you need two tubes - one for oil, another - for union suction chambers of compressors. Or one big tube which one half for oil equalization, another half for gas equalization.
    As regurds me, I prefer classic oil return system with oil separator, oil reciver and oil regulators on each compressors.
    Last edited by Aik; 23-10-2020 at 02:28 PM.
    In some places will have to think ...

  13. #13
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: 2 Compressor in 1 system

    Hi Aik
    you recommend for to use classic oil return is very good
    when one of the compressor damaged and burnouts and oil carbonated
    it doesn't effict other compressor oils.

  14. #14
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: 2 Compressor in 1 system

    you need to control both compressors to stop it freezing when the load is low

  15. #15
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: 2 Compressor in 1 system

    Thanks for all suggestions

  16. #16
    Join Date
    Feb 2021
    Location
    China
    Posts
    1
    Rep Power
    0

    Re: 2 Compressor in 1 system

    Yeah, i also think the person-located's suggestion is right, if not , the balance will not be keep.And aslo,Maybe you should learn something about the one-way valve and check valve which can provide you help.