System capacity
Dear Friends,
As you know system with sub-cooler or economizer increase system and compressor capacity, I understand this matter.
While we take some portion of liquid line to sub-cooler or economizer we also decrease our expansion valve feed but why totally twice we have capacity increase ?
Thanks.
-
13-10-2020, 08:19 PM #2
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: System capacity
Hi
Subcooling could made from different way
Heat exchange - Evaporat Water cold Condenser -
4 pipe suction aculamator- and...
Also One of them is a ECO.
In Eco. We have subcooling the liquid But main thing is cooling discharge gas in first Stage.
When we cool in first Stage we have low temperature and more mass of refrigeration for second stage.
-
13-10-2020, 09:10 PM #3
-
14-10-2020, 12:35 AM #4
Re: System capacity
This is not simple to explain ...
but each sub-cooler is not an economizer too ...
only economizers reduce power consumption and increase efficiency of refrigeration system ...
i.e. economizers are connected to screw compressor ECO port and usually increase compressor
capacity up to 20% but increase in used electric power is much less and from this
we get the name economizer ...
but, please .... read carefully this and then return to clarify if something is not clear
https://www.swep.net/refrigerant-han...systems/asdf4/
https://www.mashav-ind.co.il/sites/d...improved_0.pdf
https://en.wikipedia.org/wiki/Economizer
https://www.theseus.fi/bitstream/han...=1&isAllowed=y
Hope this will be of some help.
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
14-10-2020, 07:03 AM #5
Re: System capacity
Dear My friend,
I know exactly what is subcooler and economizer.
Installing compressor with economizer (in screw compressors) and subcooler (in two stage compressors) increase compressor capacity, It is fact and very clear.
I say my mean in very simple way, At economizer and subcooler we cool liquid line and definitely it helps us to increase compressor capacity, OK.
But question is here, Beside of cooling liquid line and increasing compressor capacity also we decrease expansion valve feed, Isn't it ?!
As you know for installing economizer/Subcooler we branch main liquid line in two ways.
One way our main liquid line that goes to evp. expansion valve and the other way goes to subcooler/economizer.
When we branch liquid line in two way, It means we decrease feeding of evaporator, Is it true ?
Now I want to know we have a positive effect means cooling liquid line and cooling compressor and negative effect we decrease expansion valve feeding.
Resultant is increasing system capacity ? Or I think in a wrong way ?
Thanks.
-
14-10-2020, 08:56 AM #6
Re: System capacity
The expansion valve feeds liquid into evaporator with sub cooled high quality liquid.
So less flash gas, but also still controls required superheat.
Less liquid could enter evaporator because less flash gas, but at same time increased refrigeration effect occurs, evaporator has more capacityLast edited by RANGER1; 14-10-2020 at 09:04 AM.
-
14-10-2020, 11:11 PM #7
Re: System capacity
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
23-10-2020, 02:44 PM #8
Re: System capacity
For understanding you may analyze simple formula:
Q=(H2-H1)*G,
Q - cooling capacity
H - entalpy of refrigerant (1 -for start evaporating process 2- for end evaporating process)
G - mass flow or refrigerant
When you have a subcooled refrigerant than you have greater entalpy difference (H2-H1). In general with subcooling entalpies defference (H2-H1) more big than decrease mass flow (G), and you can see that expension valve needs less size (becourse it regulated mass flow) and cooling capacity increase.In some places will have to think ...