    System capacity



    Dear Friends,

    As you know system with sub-cooler or economizer increase system and compressor capacity, I understand this matter.
    While we take some portion of liquid line to sub-cooler or economizer we also decrease our expansion valve feed but why totally twice we have capacity increase ?

    Thanks.



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: System capacity

    Hi
    Subcooling could made from different way
    Heat exchange - Evaporat Water cold Condenser -
    4 pipe suction aculamator- and...
    Also One of them is a ECO.
    In Eco. We have subcooling the liquid But main thing is cooling discharge gas in first Stage.
    When we cool in first Stage we have low temperature and more mass of refrigeration for second stage.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: System capacity

    Quote Originally Posted by skyboy6142 View Post
    Dear Friends,

    As you know system with sub-cooler or economizer increase system and compressor capacity, I understand this matter.
    While we take some portion of liquid line to sub-cooler or economizer we also decrease our expansion valve feed but why totally twice we have capacity increase ?

    Thanks.
    Can you explain a bit more on what you would like to know.
    Not sure what you are asking.
    Thanks

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: System capacity

    Quote Originally Posted by skyboy6142 View Post
    Dear Friends,

    As you know system with sub-cooler or economizer increase system and compressor capacity, I understand this matter.
    While we take some portion of liquid line to sub-cooler or economizer we also decrease our expansion valve feed but why totally twice we have capacity increase ?

    Thanks.
    This is not simple to explain ...

    but each sub-cooler is not an economizer too ...
    only economizers reduce power consumption and increase efficiency of refrigeration system ...
    i.e. economizers are connected to screw compressor ECO port and usually increase compressor
    capacity up to 20% but increase in used electric power is much less and from this
    we get the name economizer ...

    but, please .... read carefully this and then return to clarify if something is not clear

    https://www.swep.net/refrigerant-han...systems/asdf4/

    https://www.mashav-ind.co.il/sites/d...improved_0.pdf

    https://en.wikipedia.org/wiki/Economizer

    https://www.theseus.fi/bitstream/han...=1&isAllowed=y

    Hope this will be of some help.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    Join Date
    Jun 2020
    Location
    Malaysia
    Posts
    44
    Rep Power
    0

    Re: System capacity

    Quote Originally Posted by RANGER1 View Post
    Can you explain a bit more on what you would like to know.
    Not sure what you are asking.
    Thanks
    Dear My friend,
    I know exactly what is subcooler and economizer.
    Installing compressor with economizer (in screw compressors) and subcooler (in two stage compressors) increase compressor capacity, It is fact and very clear.

    I say my mean in very simple way, At economizer and subcooler we cool liquid line and definitely it helps us to increase compressor capacity, OK.
    But question is here, Beside of cooling liquid line and increasing compressor capacity also we decrease expansion valve feed, Isn't it ?!
    As you know for installing economizer/Subcooler we branch main liquid line in two ways.
    One way our main liquid line that goes to evp. expansion valve and the other way goes to subcooler/economizer.
    When we branch liquid line in two way, It means we decrease feeding of evaporator, Is it true ?
    Now I want to know we have a positive effect means cooling liquid line and cooling compressor and negative effect we decrease expansion valve feeding.
    Resultant is increasing system capacity ? Or I think in a wrong way ?

    Thanks.

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: System capacity

    Quote Originally Posted by skyboy6142 View Post
    Dear My friend,
    I know exactly what is subcooler and economizer.
    Installing compressor with economizer (in screw compressors) and subcooler (in two stage compressors) increase compressor capacity, It is fact and very clear.

    I say my mean in very simple way, At economizer and subcooler we cool liquid line and definitely it helps us to increase compressor capacity, OK.
    But question is here, Beside of cooling liquid line and increasing compressor capacity also we decrease expansion valve feed, Isn't it ?!
    As you know for installing economizer/Subcooler we branch main liquid line in two ways.
    One way our main liquid line that goes to evp. expansion valve and the other way goes to subcooler/economizer.
    When we branch liquid line in two way, It means we decrease feeding of evaporator, Is it true ?
    Now I want to know we have a positive effect means cooling liquid line and cooling compressor and negative effect we decrease expansion valve feeding.
    Resultant is increasing system capacity ? Or I think in a wrong way ?

    Thanks.
    The expansion valve feeds liquid into evaporator with sub cooled high quality liquid.
    So less flash gas, but also still controls required superheat.
    Less liquid could enter evaporator because less flash gas, but at same time increased refrigeration effect occurs, evaporator has more capacity
    Last edited by RANGER1; 14-10-2020 at 09:04 AM.

  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: System capacity

    Quote Originally Posted by skyboy6142 View Post
    Dear My friend,
    I know exactly what is subcooler and economizer.
    Installing compressor with economizer (in screw compressors) and subcooler (in two stage compressors) increase compressor capacity, It is fact and very clear.


    NO! Wrong .... only economizer increase actual compressor capacity due to ECO port connectiton ... the same compressor gives around 20% more capacity but we need to imput 12% more electric power ... end economizer we can utilize only with screws
    it is not necessary to be a two stage plant to utilize economizer as subcooler and again get a more capacity with SINGLE compressor ... nominal capacity for cooling and additional capacity through ECO port


    If not connected to ECO port then we have subcooler helping also to reduce flash gas, but actual compressor capacity for cooling is reduced due to part load for subcooler and here we can use other than screw compressors to do the work ... compressor must be with bigger capacity calculated both for cooling and for subcooling and we have to pay full price


    I say my mean in very simple way, At economizer and subcooler we cool liquid line and definitely it helps us to increase compressor capacity, OK. YES and NO!
    But question is here, Beside of cooling liquid line and increasing compressor capacity also we decrease expansion valve feed, Isn't it ?!
    NO! We need to calculate feeding line to be big enough for expansion valve and for economizer otherwise plant will not work.


    As you know for installing economizer/Subcooler we branch main liquid line in two ways.
    One way our main liquid line that goes to evp. expansion valve and the other way goes to subcooler/economizer.
    When we branch liquid line in two way, It means we decrease feeding of evaporator, Is it true ? NO! We do not decrease feeding line ... system will not work.
    Now I want to know we have a positive effect means cooling liquid line and cooling compressor and negative effect we decrease expansion valve feeding.
    Resultant is increasing system capacity ? Or I think in a wrong way ?
    Yes, a little bit wrong

    Thanks.
    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  8. #8
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: System capacity

    Quote Originally Posted by skyboy6142 View Post
    Dear Friends,

    As you know system with sub-cooler or economizer increase system and compressor capacity, I understand this matter.
    While we take some portion of liquid line to sub-cooler or economizer we also decrease our expansion valve feed but why totally twice we have capacity increase ?

    Thanks.
    For understanding you may analyze simple formula:
    Q=(H2-H1)*G,
    Q - cooling capacity
    H - entalpy of refrigerant (1 -for start evaporating process 2- for end evaporating process)
    G - mass flow or refrigerant
    When you have a subcooled refrigerant than you have greater entalpy difference (H2-H1). In general with subcooling entalpies defference (H2-H1) more big than decrease mass flow (G), and you can see that expension valve needs less size (becourse it regulated mass flow) and cooling capacity increase.
    In some places will have to think ...