    Some times I see cold rooms that evaporator has been installed above doors ! I think this place is best place that we can use for evaporator without occupying room for goods.
    But I was reading a bulletin of Heatcraft factory, I saw on this "NEVER install evaporator over doors !" .

    What is your opinion about this ?

    Thanks.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: evaporator above doors

    I would suggest that it is a location that has the highest humidity due to the incoming outside air which could encourage early icing of the coil.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: evaporator above doors

    Always on the wall facing the door or on the side wall.
    If you install it over the door, every time you open it, it sucks hot humid air with all the dirt in the air.