Results 1 to 3 of 3
Thread: evaporator above doors
-
29-09-2020, 10:46 AM #1
evaporator above doors
Dear friends,
Some times I see cold rooms that evaporator has been installed above doors ! I think this place is best place that we can use for evaporator without occupying room for goods.
But I was reading a bulletin of Heatcraft factory, I saw on this "NEVER install evaporator over doors !" .
What is your opinion about this ?
Thanks.
-
29-09-2020, 03:58 PM #2
Re: evaporator above doors
I would suggest that it is a location that has the highest humidity due to the incoming outside air which could encourage early icing of the coil.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
29-09-2020, 04:21 PM #3
Re: evaporator above doors
Always on the wall facing the door or on the side wall.
If you install it over the door, every time you open it, it sucks hot humid air with all the dirt in the air.
Bad practice.