    Dear All

    In a refrigeration air dryer the refrigerant Compressor MANEUROP MTZ72HN4AVE burnt and must be replaced. In the local market I didn't find the same compressor but I found the model MANEUROP MTZ80HN4AVE (little bigger).

    Its ok to replace the refrigerant Compressor MANEUROP MTZ72HN4AVE by MANEUROP MTZ80HN4AVE.

    I am waiting your comments.

    Best rgards



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Replacement of r404a compressor

    You did not state what refrigerant is in the system but any other make for the same refrigerant and POE oil, with the same pistons volume will do.