    May 2009
    New Zealand
    141
    15
    Cold trap on NH3
    Hi, do ice traps work on ammonia systems for removing water? Water ends up in the coldest part of the system so if you made a colder part would the water migrate there? Cheers.
    Sep 2014
    usa
    1
    Re: Cold trap on NH3
    I suggest installing an H.A. Phillips Anhydrator System Cleaner. It basically traps contaminants such as water. You can get information on how it works on their website
    3,355
    We are cheapskates, we have a spare ammonia portable vessel.
    Fill if up 50 %, let it vent naturally back into system.
    Do that a number of times, drain water off, check amount.
    Keep doing that until no water left.
    Get client to keep filling, over a few weeks or so should get less & less. MJust need a suitable spare ammonia vessel.
    Jul 2006
    73
    865
    26
    What works well is an oil trap under a Low Pressure Receiver. Vent it off as RANGER1 suggests.
    I had a system years ago that split a oil cooler for a Vilter piston machine. We found a lot of the water eventually ended up in the Intercooler.
    May 2009
    New Zealand
    141
    15
    Thanks all. I have experience with the above methods and I’m a cheapskate too hence wanting to try the cold trap. I’ll see if the client is keen for me to give it a go and I will report back.