Thread: carrier freeze protection fault
-
16-09-2020, 02:20 PM #1
carrier freeze protection fault
Hi All,
I have a carrier twin screw aircooled chiller that keep failing on freeze protection at night when it has no run command.
Any ideas of what could cause this fault?
-
16-09-2020, 03:34 PM #2
Re: carrier freeze protection fault
What is the nighttime ambient temperature?
Have you checked the setting/operation of the fluid low temperature switch?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
16-09-2020, 06:54 PM #3
Re: carrier freeze protection fault
Are the pumps running at night
-
21-09-2020, 02:56 PM #4
Re: carrier freeze protection fault
the night ambients are always above 0 degrees and the problem happens all year round when the overnight temp would be above 10 degrees
-
21-09-2020, 02:58 PM #5
Re: carrier freeze protection fault
the chiller has onboard pumps so I dont think they run at night.
I removed the plug for remote running of the chiller so it did not get a call to run from anywhere.
-
21-09-2020, 04:47 PM #6
Re: carrier freeze protection fault
Chiller must have "black box" in its controller. can u check data at moment of fault?