    Neutrel switching



    Thanks for your thoughts the last time i visited the forum,ive decided the engineers route, problem is ive hit my first brickwall?

    I,m fine with live switching and fault finding but how do you test a circuit that controls by switching NEUTRALS with my multi meter.

    any help much apprciated.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Neutrel switching

    Can you give us an example of a circuit that uses neutral switching in the UK?

  3. #3
    rbartlett's Avatar
    rbartlett Guest

    Re: Neutral switching

    Quote Originally Posted by frank
    Can you give us an example of a circuit that uses neutral switching in the UK?
    A lot of old Italian counters plus the odd American bit switched on the netural...it can be very difficult as we are trained to look for the end of the 'live' to find where the fault lies but with neutral switching it can be very confusing and potentially lethal..

    For testing a t.stat for example. the 'dead' leg will -supposedly-be incoming, the way is to put the tester either side of the switch and check for voltage across as you would normally.

    It can be best to work from the live side and see where it goes dead you just have to be a bit more careful.

    For practise if you have a working cabinet accessible to play with, just swap the live for the neutral in the plug and see what happens

    cheers

    richard

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Neutrel switching

    I've only come across a neutral switch once. It was on an old American time clock. Strange way of doing it, and as you say, it could be dangerous. Goes against all your instincts when trouble shooting.

  5. #5
    Join Date
    Jun 2006
    Location
    Leicester
    Age
    34
    Posts
    18
    Rep Power
    0

    Re: Neutral switching

    I;ve come across this problem on 2 new zanussi cabinets this week alone and they were commercial cabinets,also on a Zanotti coldroom.I will try your idea Richard of swapping the plug wires if it goes bang ne sweat.

    cheers

    Wizzer

  6. #6
    Join Date
    Mar 2005
    Location
    uk
    Age
    54
    Posts
    42
    Rep Power
    0

    Re: Neutrel switching

    Is switching the neutral, not against IEE regs

  7. #7
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Neutrel switching

    Hi Guys

    Reeferjon and MRW will know more about this than i do but i am sure some TK SR units use neutral switching on the control circuits

    Regards

    Fatboy

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Neutrel switching

    PE switching is against the regulation, not neutral switching.

  9. #9
    Join Date
    Oct 2004
    Location
    uk
    Age
    56
    Posts
    193
    Rep Power
    20

    Re: Neutrel switching

    if you follow the control circuit from the end backwards wouldn't the break be showm by a backfeed of 240v or whatever the control voltage is.
    i do agree that live switching is easier to follow but a lot of continental cabinets used to be neutral switched and as long as there were no electronic controls we just used to reverse the cables at the cabinet, not in the plug and we always marked the system for the next engineer

    happy to help
    bill

  10. #10
    Join Date
    Jun 2006
    Location
    Alberta
    Age
    36
    Posts
    21
    Rep Power
    0

    Re: Neutrel switching

    99% of the mechanical timeclocks used for defrost termination switch on the neutral side, it is one of the rare occasions where it is allowed in Canada.

  11. #11
    Decdastardly's Avatar
    Decdastardly Guest

    Re: Neutrel switching

    I see neutral switching sometimes on icemachines, scotsman mainly it definately makes fault finding awkward..don't really see why they do that -maybe to reduce arcing at the switch was my only thought or maybe just certain manufacturers convention

  12. #12
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,700
    Rep Power
    46

    Re: Neutrel switching

    Quote Originally Posted by Decdastardly View Post
    I see neutral switching sometimes on icemachines, scotsman mainly it definately makes fault finding awkward..don't really see why they do that -maybe to reduce arcing at the switch was my only thought or maybe just certain manufacturers convention
    Nice of you to join in Dec.
    May I just point out that this post was last added to in June 2006.
    Perhaps a newer one next time may have more people contribute?
    Welcome anyways!
    Grizzly

  13. #13
    Decdastardly's Avatar
    Decdastardly Guest

    Re: Neutrel switching

    Ha! spot the rookie poster!

  14. #14
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Neutrel switching

    Quote Originally Posted by Decdastardly View Post
    Ha! spot the rookie poster!

    its you .
    Takes a licking, keeps on ticking.