    McQuay screw chiller



    Hi friends

    I have a McQuay chiller Model : AWS49000 with three compressors model HSA263QS24YA
    one compressor trips on hi oil pressure deferential, I replaced oil filter two times and the oil pressure transducer and recharched new oil but no change on situation (taking into consideration that the old oil was dirty) , it looks like that insufficient oil is reaching filter.
    My question is that could the oil separator be a reason for this case, or there may be another reason , please help me to solve this problem & thanks in advance



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: McQuay screw chiller

    IT can be a few things: Oil pump failure, insufficient refrigerant, partially blocked drier and oil separator, TXV not function OK.

    Check carefully temp and pressure along the refrigerant lines and components.

  3. #3
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    16

    Re: McQuay screw chiller

    Did you check pressure drop across oil filter? is it really higher than 250kPa? And I dont think it can be oil separator. this alarm is generated by two pressure sensors, before and after oil filter. If this value higher than 250 kPa (or setpoint what is in your case) compressor stops.

  4. #4
    Join Date
    Jun 2017
    Location
    Norway
    Posts
    32
    Rep Power
    0

    Re: McQuay screw chiller

    What is the oil temprature?