    Placing the condensing unit away from the reach in refrigerator.



    Hello guys.
    My customer wants to remove his condensing u nits from inside the store and place them
    Outside on the rooftop. About 10_ 15m away.
    My concern is that those units are all cap tube.
    Can it be done. With out changing with tev, and a receiver. And if I change that Will it work. The compressor s are 1/3,
    I am waiting for your response.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Placing the condensing unit away from the reach in refrigerator.

    If the cap the starts at the condensing unit outlet then extend the liquid line from the condenser to the start of the cap line. Refrigerant charge will need adjusting of course. Would be worth adding a sight glass to the line as well.

    Ensure that the new refrigerant total does not exceed the maximum allowed by the compressor, fit a crankcase heater.
    Last edited by Brian_UK; 05-08-2020 at 12:00 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Placing the condensing unit away from the reach in refrigerator.

    You will have to install a liquid receiver and a txv . An sv before the txv will help protect the compressor from floodback.