    Trane RTWD 250, compressor failed to start:transition



    Hi all,

    Had a quick look but nothing popped out to me.

    Having the above issue with a Trane rwtd250 Chiller.

    Trying to run the comp, the star contactor pulls in then out and in a bit, (I know lol) delta contactor pulls in and the compressor just sits there humming like it is stalling and needs a booting.

    Has anyone here had the same issues or maybe some experience to resolve this please?

    Recently replaced the HP switch on the circuit and pumped down the compressor, placed fridge back in and attempted to run then this issue appeared.

    Any help appreciated, thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Trane RTWD 250, compressor failed to start:transition

    Sounds like the star/delta timer needs replacing.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2017
    Location
    Essex
    Age
    44
    Posts
    81
    Rep Power
    7

    Re: Trane RTWD 250, compressor failed to start:transition

    Ah yeah makes sense actually now thinking about it. Strange how it all happened.

    Thank you Brian, I’ll give that a shot see what happens.

  4. #4
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Trane RTWD 250, compressor failed to start:transition

    Pull the comp fuses and run it , check the continuity through the contactors