Hi All
I have two undercounter fridges, both sharing one condenser.
A few weeks ago, one of the fridges TXV started to freeze heavily. I allowed it to thaw, and restarted the fridge. Within 15 minutes it was a solid ball of ice again. I switched the fridge off and left as it wasn’t a desperate repair. Last week I was called to look at the other freezer on the same condenser and found the exact same thing happening.
I plan to reclaim tomorrow and reluctantly swap out both valves and driers, though it’s going to be a real pig of a job. The valve are preset and cannot be adjusted.
Anything I’m missing? I find it a tad too coincidental that both valves are misbehaving.
Thanks in advance
-
12-07-2020, 09:58 PM #2
Re: TXV Icing Up
Short of gas?
TXV strainers blocked?
Filter/driers blocking, check temperatures?
Airflows?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
12-07-2020, 10:26 PM #3
Re: TXV Icing Up
I would check to see if there was a large Temperature difference across the Drier first. This would explain everything.
-
13-07-2020, 09:24 PM #4
Re: TXV Icing Up
Moisture in the system?
Mostly found in Oxfordshire, UK :)
-
13-07-2020, 09:44 PM #5
Re: TXV Icing Up
Thanks boys
Found the unit with only 400g of a 2kilo charge. Fingers crossed I’ll find and repair the leak tomorrow and fill her back up. See if that makes a difference.
-
14-07-2020, 12:11 AM #6
Re: TXV Icing Up
Yep, correct charge could well make a difference.
Brian - Newton Abbot, Devon, UK
Retired March 2015