Results 1 to 6 of 6

Thread: TXV Icing Up

  1. #1
    Join Date
    Feb 2013
    Location
    United Kingdom
    Posts
    2
    Rep Power
    0

    Question TXV Icing Up



    Hi All

    I have two undercounter fridges, both sharing one condenser.

    A few weeks ago, one of the fridges TXV started to freeze heavily. I allowed it to thaw, and restarted the fridge. Within 15 minutes it was a solid ball of ice again. I switched the fridge off and left as it wasn’t a desperate repair. Last week I was called to look at the other freezer on the same condenser and found the exact same thing happening.

    I plan to reclaim tomorrow and reluctantly swap out both valves and driers, though it’s going to be a real pig of a job. The valve are preset and cannot be adjusted.

    Anything I’m missing? I find it a tad too coincidental that both valves are misbehaving.

    Thanks in advance



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: TXV Icing Up

    Short of gas?

    TXV strainers blocked?

    Filter/driers blocking, check temperatures?

    Airflows?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: TXV Icing Up

    I would check to see if there was a large Temperature difference across the Drier first. This would explain everything.

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: TXV Icing Up

    Moisture in the system?
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    Feb 2013
    Location
    United Kingdom
    Posts
    2
    Rep Power
    0

    Re: TXV Icing Up

    Thanks boys

    Found the unit with only 400g of a 2kilo charge. Fingers crossed I’ll find and repair the leak tomorrow and fill her back up. See if that makes a difference.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: TXV Icing Up

    Yep, correct charge could well make a difference.
    Brian - Newton Abbot, Devon, UK