    Daikin R32 MultiSplit Issue



    Hi,

    We recently replaced a customers old R22 Inverter Daikin Multisplit with a Brand new R32 Inverter System.

    The customer has complained that, if using one of the 3 units on heat, the other two indoor units coils are heating up/cooling (not switching on, but refrigerant is flowing to them).

    We have not attended yet, no other multi splits we have installed have worked this way.

    Thoughts Welcome Please?

    TM



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Daikin R32 MultiSplit Issue

    Fujitsu multi's do the same thing. Hot gas goes to each coil and if the EEV of unused fan coils are closed the oil can get trapped. Unused fan coils have the EEV slightly open to avoid this so the coil will get warm as a result.

  3. #3
    Join Date
    Oct 2007
    Location
    Manchester
    Posts
    15
    Rep Power
    0

    Re: Daikin R32 MultiSplit Issue

    Many Thanks

  4. #4
    Join Date
    Jan 2020
    Location
    EU
    Posts
    25
    Rep Power
    0

    Re: Daikin R32 MultiSplit Issue

    Quote Originally Posted by Tayters View Post
    Fujitsu multi's do the same thing. Hot gas goes to each coil and if the EEV of unused fan coils are closed the oil can get trapped. Unused fan coils have the EEV slightly open to avoid this so the coil will get warm as a result.
    Where does the oil get trapped if the EEV is closed? In liquid line?

  5. #5
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Daikin R32 MultiSplit Issue

    Not sure exactly where it’ll get trapped and thinking about it, if the EEV was closed then theoretically there will be no flow therefore no carried over oil?
    I’m guessing oil concentration will be somewhere in the hot gas pipes near the outdoor unit and oil would sit in any low parts of the pipework .
    Last edited by Tayters; 24-06-2020 at 12:25 AM.

  6. #6
    Join Date
    Oct 2013
    Location
    Ukraine
    Posts
    14
    Rep Power
    0

    Re: Daikin R32 MultiSplit Issue

    Quote Originally Posted by Glide View Post
    Where does the oil get trapped if the EEV is closed? In liquid line?
    The gas line is discharge line and the oil will get trapped in the indoor coil and further towards the compressor, if EXV will be fully closed. VRF systems work with the same principle.