Results 1 to 10 of 10
    Oct 2007
    Manchester
    15
    Everything seems right but not freezing? Old Style with fuzzy logic
    Despite 30 years of experience, I am struggling with something that is driving me mad.
    I have a customer with an AGA upright frost free freezer (commercial style domestic).
    It has electronic control with reverse gas defrost. All that is working fine, its just not refrigerating.
    The system is fully charged (has been evacuated and recharged with R134a). It was probably charged okay to begin with.
    The running back pressure is just above zero, this indicates an evaporating temperature of around -23c.
    As its a freezer, I was expecting and evaporations TD of around 10-15c. So therefore, I initially expected a back pressure of -10psi(g).
    Speaking to colleagues, they suggest the back pressure of around zero is okay?.
    Please can someone help me out here?
    Regards,
    TM
    Feb 2011
    scotland
    454
    Re: Everything seems right but not freezing? Old Style with fuzzy logic
    Fin tube evap coil with fan?
    Capillary tube or expansion valve or EEV?
    3,357
    Quote Originally Posted by teemyob View Post
    Regards,
    TM
    TM,
    First, a TD of 10 to 15Deg C is out of the question.
    More like 3 to 4 deg C.
    So with -23 deg C suction, expect at least around -18 deg C
    You say not refrigerating, so what is current temperature?
    If you measurer air on/off you can tell if it is doing anything.
    Is evaporator definitely defrosted?
    Is door seal sealing correctly
    Oct 2001
    Nottingham UK
    5,668
    R134a with a capillary expansion device can become blocked (oil flocced) over time.
    Although you have low temps on the evap I would suspect that with a blocked capillary, you have restriced flow and a starved evaporator leading to high temps in the box.
    Oct 2007
    Manchester
    15
    Quote Originally Posted by seanf View Post
    Capilliary Tube
    Oct 2007
    Manchester
    15
    Sounds feasible
    Oct 2007
    Manchester
    15
    TM,
    Thank you
    Slight sweating on fin evaporator
    air off barely lower than room temp
    door 100%
    Sep 2003
    ISRAEL
    72
    4,248
    I totally agree with Frank. Its blocked somewhere.
    Bear in mind that R-134 is a fantastic cleaning agent and have more blockage problems then most refrigerants.
    Can you install a TXV instead of the capillary tube ?
    Oct 2007
    Manchester
    15
    hi, thanks everyone.
    Sadly no room!
    Feb 2011
    scotland
    454
    What about a fixed orifice?