    Everything seems right but not freezing? Old Style with fuzzy logic



    Hi,

    Despite 30 years of experience, I am struggling with something that is driving me mad.

    I have a customer with an AGA upright frost free freezer (commercial style domestic).

    It has electronic control with reverse gas defrost. All that is working fine, its just not refrigerating.

    The system is fully charged (has been evacuated and recharged with R134a). It was probably charged okay to begin with.

    The running back pressure is just above zero, this indicates an evaporating temperature of around -23c.

    As its a freezer, I was expecting and evaporations TD of around 10-15c. So therefore, I initially expected a back pressure of -10psi(g).

    Speaking to colleagues, they suggest the back pressure of around zero is okay?.

    Please can someone help me out here?

    Regards,
    TM



  2. #2
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    453
    Rep Power
    17

    Re: Everything seems right but not freezing? Old Style with fuzzy logic

    Fin tube evap coil with fan?
    Capillary tube or expansion valve or EEV?
    Last edited by seanf; 19-06-2020 at 07:07 PM.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Everything seems right but not freezing? Old Style with fuzzy logic

    Quote Originally Posted by teemyob View Post
    Hi,

    Despite 30 years of experience, I am struggling with something that is driving me mad.

    I have a customer with an AGA upright frost free freezer (commercial style domestic).

    It has electronic control with reverse gas defrost. All that is working fine, its just not refrigerating.

    The system is fully charged (has been evacuated and recharged with R134a). It was probably charged okay to begin with.

    The running back pressure is just above zero, this indicates an evaporating temperature of around -23c.

    As its a freezer, I was expecting and evaporations TD of around 10-15c. So therefore, I initially expected a back pressure of -10psi(g).

    Speaking to colleagues, they suggest the back pressure of around zero is okay?.

    Please can someone help me out here?

    Regards,
    TM
    TM,
    First, a TD of 10 to 15Deg C is out of the question.
    More like 3 to 4 deg C.
    So with -23 deg C suction, expect at least around -18 deg C

    You say not refrigerating, so what is current temperature?
    If you measurer air on/off you can tell if it is doing anything.
    Is evaporator definitely defrosted?
    Is door seal sealing correctly

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Everything seems right but not freezing? Old Style with fuzzy logic

    R134a with a capillary expansion device can become blocked (oil flocced) over time.

    Although you have low temps on the evap I would suspect that with a blocked capillary, you have restriced flow and a starved evaporator leading to high temps in the box.

  5. #5
    Join Date
    Oct 2007
    Location
    Manchester
    Posts
    15
    Rep Power
    0

    Re: Everything seems right but not freezing? Old Style with fuzzy logic

    Quote Originally Posted by seanf View Post
    Fin tube evap coil with fan?
    Capillary tube or expansion valve or EEV?
    Capilliary Tube

  6. #6
    Join Date
    Oct 2007
    Location
    Manchester
    Posts
    15
    Rep Power
    0

    Re: Everything seems right but not freezing? Old Style with fuzzy logic

    Sounds feasible

  7. #7
    Join Date
    Oct 2007
    Location
    Manchester
    Posts
    15
    Rep Power
    0

    Re: Everything seems right but not freezing? Old Style with fuzzy logic

    Quote Originally Posted by RANGER1 View Post
    TM,
    First, a TD of 10 to 15Deg C is out of the question.
    More like 3 to 4 deg C.
    So with -23 deg C suction, expect at least around -18 deg C

    You say not refrigerating, so what is current temperature?
    If you measurer air on/off you can tell if it is doing anything.
    Is evaporator definitely defrosted?
    Is door seal sealing correctly

    Thank you

    Slight sweating on fin evaporator
    air off barely lower than room temp
    door 100%

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Everything seems right but not freezing? Old Style with fuzzy logic

    I totally agree with Frank. Its blocked somewhere.
    Bear in mind that R-134 is a fantastic cleaning agent and have more blockage problems then most refrigerants.

    Can you install a TXV instead of the capillary tube ?

  9. #9
    Join Date
    Oct 2007
    Location
    Manchester
    Posts
    15
    Rep Power
    0

    Re: Everything seems right but not freezing? Old Style with fuzzy logic

    Quote Originally Posted by chemi-cool View Post
    I totally agree with Frank. Its blocked somewhere.
    Bear in mind that R-134 is a fantastic cleaning agent and have more blockage problems then most refrigerants.

    Can you install a TXV instead of the capillary tube ?
    hi, thanks everyone.

    Sadly no room!

  10. #10
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    453
    Rep Power
    17

    Re: Everything seems right but not freezing? Old Style with fuzzy logic

    What about a fixed orifice?