Results 1 to 2 of 2
  1. #1
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Head Temperature



    Hi Seniors,
    Here in the summer season head Temperature increasing upto 135'C . Especially head number 01 others 125'C.
    Why it is manual says maximum discharge temperature 170'C. Boss little frightened. Compressor Grasoo R 612
    Suction pressure 2.6Bar
    Discharge pressure 13Bar
    What is allowable discharge head Temperature.

    Awaiting your kind words.



  2. #2
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    223
    Rep Power
    19

    Re: Head Temperature

    Hi Shaaf,
    at your conditions, -4.6 / + 36.3°C; standard mineral oil, 1000tr/mn, superheat 2°K, ambiant 40°C.
    theoretical discharge temp is 114.3°C.
    at 6°K superheat, discharge is 119.9°C.
    In your case, 135°C is too high but N°1 is at the opposite of suction connection so a bit warmer than the second cylinder bank.
    check for any discharge/suction valve issue.
    170°C is the maximum discharge temperature when the compressor is fitted with cylinder heads probes. it's the temperature close to the discharge valves. when one breaks the temperature rise suddently
    RC9;11;12;12E were fitted with those cylinder probes connected to a TSU.
    on the discharge pipe 140°C is the usual max temperature with discharge pipe sensor.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •