Results 1 to 5 of 5
  1. #1
    Join Date
    Feb 2004
    Location
    yorkshire
    Age
    42
    Posts
    33
    Rep Power
    0

    Oil Washing out of compressor



    Hi all,

    I have some compressors having the oil wash out of the compressor and then the compressor seizing up. It is on static cooling (non forced air) it has a condenser with fan but frozen shelves.

    unit is on r290 and it has a danfoss compressor on, they doesnt seam to be much sub cooling and the compressor does get really, also the drier gets really hot when the ambiant is only around 18oc


    hello its me

  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Oil Washing out of compressor

    Are the shelves supposed to be iced up? Is the compressor rated for low back pressure? Is your condenser spotless with fans running at full speed? is condensing unit outside or internal? Any pressures/temps?
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Oil Washing out of compressor

    have you checked super heat to make sure it not flooding

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Oil Washing out of compressor

    is this a new system or has it just started to have issues

  5. #5
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Oil Washing out of compressor

    Has the suction line been oil trapped or had a suction accumulator fitted. Is the condensing unit above or below the evaporator and how long is the suction