    I have a 96 Phoenix Carrier Unit that I'm needing some help with. This unit has worked just fine the last 6 months but I let it set for 10 days without running it and now it won't cool down. Coolant reaches 150 after about 10 minutes or so, and the suction line is reading -5 to -6. I really just don't have a clue and any help would be appreciated.



  2. #2
    novel.harris's Avatar
    novel.harris Guest

    Re: Phoenix Carrier Reefer Unit Trouble

    hello am Novel and am in Afghan with a model 69nt40-5013 reffer manufa. 4/95 need help to clear alarm 52 it will not start am in the army a need help.

  3. #3
    Join Date
    Jan 2006
    Location
    United Kingdom
    Age
    60
    Posts
    11
    Rep Power
    0

    Re: Phoenix Carrier Reefer Unit Trouble

    Make sure that there are no other active alarms other than AL52 (alarm list full) in alarm list.
    Select "Alt Mode" parameter "DC30" and press enter for 5 seconds to zero trip start then clear alarm list as normal.

    Best Regards
    Ian

  4. #4
    Join Date
    Nov 2001
    Location
    Shropshire
    Age
    59
    Posts
    260
    Rep Power
    23

    Re: Phoenix Carrier Reefer Unit Trouble

    Possible shaft seal leak on the compressor resulting in loss of refrigerant....is there a lot of oil round the shaft that enters the compressor......you will need to fit gauges to check pressures.

    John.




    Quote Originally Posted by razorback76
    I have a 96 Phoenix Carrier Unit that I'm needing some help with. This unit has worked just fine the last 6 months but I let it set for 10 days without running it and now it won't cool down. Coolant reaches 150 after about 10 minutes or so, and the suction line is reading -5 to -6. I really just don't have a clue and any help would be appreciated.

  5. #5
    razorback76's Avatar
    razorback76 Guest

    Re: Phoenix Carrier Reefer Unit Trouble

    thank you reeferjon!

Similar Threads

  1. Container Reefer Unit for Controlled Atmosphere (CA)
    By reeferman in forum New Technologies
    Replies: 9
    Last Post: 26-08-2011, 09:26 AM
  2. Daikin a/c units.
    By rick in forum Air Conditioning
    Replies: 59
    Last Post: 18-02-2008, 09:22 PM
  3. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  4. Zanotti Units
    By Carlo Hansen in forum Transport
    Replies: 3
    Last Post: 27-05-2006, 08:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •