Results 1 to 9 of 9
    May 2011
    India
    38
    106
    13
    Vapour pressure and saturation temperature - Estimate qunatity
    How can we estimate the liquid quantity in a jug, by knowing its pressure and temperature?
    11,025
    Re: Vapour pressure and saturation temperature - Estimate qunatity
    If by jug you mean a refrigerant cylinder then simply weigh it and subtract the tare weight to give the weight of the contents.
    May 2011
    India
    38
    106
    13
    Yeah, but how exactly do I know what percentage is liquid and gas? The PT chart would show the refrigerant within the saturation curve, but how can I estimate the liquid/gas percentage....
    Feb 2011
    scotland
    452
    The way Ive seen it done is,
    - Find the specific volume of the total contents -
    v = Volume of cylinder / Mass of the refrigerant (vapour and liquid)
    - Use the refrigerants property tables to find the specific volumes of the vapour and of the liquid at the saturation temp/pressure. -
    vg - specific volume of the vapour
    vf - specific volume of the liquid
    - Find the Quality -
    x = (v - vf) / (vg - vf)
    - The mass of vapour is then found -
    Mass of vapour = (quality) X (total mass (liquid and vapour))
    You can work out the rest from that.
    The above is given as an example in the book, Thermodynamics: An Engineering Approach, Çengel/Boles, 8th edition, page 129, Properties of Saturated Liquid-Vapour Mixture. More than likely to find it online for free.
    11,025
    Or, tap the side of the cylinder with a small spanner moving slowly from the base up to the top. When the sound note changes then you have found the top of the liquid.
    Oct 2008
    newbury
    1,444
    37
    This is a test or homework question not a out in the field one :-)
    May 2011
    India
    38
    106
    13
    Thanks a lot guys! I was just being curious whenever I see a liquid receiver. Now it makes some sense :-)
    May 2011
    India
    38
    106
    13
    haha... definitely not in field.
    Jan 2006
    Croatia
    68
    2,261
    31
    Quote Originally Posted by nevinjohn View Post
    Here you can read a little more all about: ... easy way ... all is within RE forums
    http://www.refrigeration-engineer.co...iquid-receiver
    http://www.refrigeration-engineer.co...-receiver-size
    http://www.refrigeration-engineer.co...8&d=1466916864
    best regards,
    Josip