    Re: High Temp Heat Pumps



    Quote Originally Posted by NoNickName View Post
    Refrigerants which would thermodinamically work at those temperature are made up of heavy molecules. The two most promising, from a rapid research, are RC318 (AKA octafluorocyclobutane, C4F8) or R718 (AKA water).
    Water and compressor are not for love making!



  2. #52
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: High Temp Heat Pumps

    I took a quick look at iso-butane. The pressure ratio would be about 2.4:1 and a differential pressure of 230 psi (~15 bar).

    So it would need a steel case and some other special requirements.

    I still think this is in the realm of possible... But it's going to take more time than 15-20 minutes to development a solid plan.
    If all else fails, ask for help.


  3. #53
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: High Temp Heat Pumps

    How is it going with your high temp heat pump US Iceman?

  4. #54
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: High Temp Heat Pumps

    Hi SteinarN.

    I have not started on it yet.

    I have been waiting for some information from the client. Not sure why they are taking so long, but will be investigating the reasons for the delay.
    If all else fails, ask for help.


  5. #55
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: High Temp Heat Pumps

    What capasity is it supposed to have?

  6. #56
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: High Temp Heat Pumps

    Somwhere around 0.9 MW cooling, therefore the heating will be slightly higher.
    If all else fails, ask for help.


  7. #57
    rsandor's Avatar
    rsandor Guest

    Re: High Temp Heat Pumps

    I`m new here and also interested in high temp output heat pumps.
    My house is already heated by panel radiators running from a gas fired boiler. Already changed windows/doors, improved outer insulation of walls. It would be great investment to make floor/wall heating, hardly to add more radiators. The total capacity of radiators are near calculated heat load of house (around 16kW on 80m2), so on cold days (we have about 7 days with -20C yearly) 80C of forward water (don`t know the return temp and flowrate) is required to maintain 22C in house. I heard that some improvements are made in heat pump technology, and it is now possible to achive higher water temperatures with reasonable COP/EER. Maybe with carbon-dioxide based HP? Advice me would it be economical to invest in vertical closed loop GSHP with the existing heating system?

  8. #58
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    45
    Posts
    54
    Rep Power
    19

    Re: High Temp Heat Pumps

    Heat pumps for domestic use are very en-vogue at the mo everyone is talking about ground source/ domestic hot water etc.

    Sadly gas/oil boilers are always going to be much cheaper to buy because there are less components and public demand is far greater.

    only when gas /oil are no longer widely available will electrcity (by nuclear or coal power stns) become comparatively cheap. Until this time heat pumps aren't economically viable. For the home at least.

    In Japan electricity is cheaper than gas or oil so domestic hp are widely available. For the last 10 yrs they have developed a co2 heat pump which can heat water efficiently see below link.


    http://en.wikipedia.org/wiki/EcoCute


    The japs are far ahead of the race

  9. #59
    rsandor's Avatar
    rsandor Guest

    Re: High Temp Heat Pumps

    Thx aeb200! Following Your link I found very useful site ...r744... and disappointingly for me the next answer regarding space heating by Dr. S. Girotto:
    "...It must be stressed that many people, listening about the features of this product, are attracted by high temperatures of water (i.e. 80°C) at the end
    of process and erroneously believe that it is possible to use a CO2 heat pump to supply hot water to a space heating system operating, as an example, with
    radiators, with return temperature relatively high, i.e. 55-60°C.
    This is not possible, as a CO2 heat pump is not suited for high temperature space heating system, due to high return temperature required by these solutions.
    High return temperature means higher temperature of CO2 at the end of heat rejection process (i.e with return water at 50°C CO2 temperature at gas cooler
    out would be approximately 55°C) and consequently very poor efficiency and capacity..."
    Is that the final word for my problem? No reasonable way of converting heat form range 10-80C to range 80-55C?

  10. #60
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: High Temp Heat Pumps

    That is not true. The efficiency drop as the return water increases, but this has nothing to do with the feasibility or not.

  11. #61
    ian g's Avatar
    ian g Guest

    Re: High Temp Heat Pumps

    Has anyone had a look at the mitsi high temp unit that gos on the R2 heat recovery vrf . I am looking to put in 7 of them in a hotel to do all the hot water I should get 12.5 KW from each one with temps up to 70C but does it work as have only had feedback from mitsi own canteen ?

  12. #62
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,554
    Rep Power
    26

    Re: High Temp Heat Pumps

    Hi Us iceman,
    can give you 85C water no problem, (design unit for dairy CIP cleaning the milk pipes!), can get partial steam, but the vapour gets trapped in the heat exchanger, head pressure becomes uncontrollable! Continuus running we can achieve mid 90C with occassional steam bubbles.
    This unit for the dairy farms can have an effective COP of just under 10, in most cases around 7
    Copeland scroll within normal operating envelope

  13. #63
    cooper3305's Avatar
    cooper3305 Guest

    Re: High Temp Heat Pumps

    Could anybody explain the effects of a low temp around -2degc ground source loop on a hp (r410a) running in heating mode? will the condenser/source heat exchanger have slugging refrigerant if the TXV is undersized? I have considered changing the superheat setting but as this is an extreme seasonal problem i am hoping for some insperation.

  14. #64
    GreenCool's Avatar
    GreenCool Guest

    Thumbs up Re: High Temp Heat Pumps

    Hi Guys,

    Probably far bigger than you were interested in but this graphic is of an ammonia heat pump being designed for a city in Norway.

    >14MW heating from 60C to 90C, by cooling down the Fjord!

    search youtube for

    star-drammen-heatpump

    hot stuff

    all the best

    GC

  15. #65
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: High Temp Heat Pumps

    Very nice...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  16. #66
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: High Temp Heat Pumps

    Take a look at daikin new altherma (trying to kick mitubishi's but for the zubadan no offense to "VRVIII" ) i don't know it it's released yet but you might find some info they say it is going up to 80 deg C i think it's 2 stage like the mitsubishi VRF "booster unit" (2 stage, one stage from the VRF system and another compressor in the unit for the second stage)that delivers up to 70 deg C water temp.

    I had the idea for doing this some time ago as i design heat pumps, but i did not see the need for such a hight condensing temp

  17. #67
    Join Date
    Sep 2005
    Location
    India
    Age
    49
    Posts
    30
    Rep Power
    0

    Re: High Temp Heat Pumps

    Hello Iceman,
    Did you make any progress in these heat pumps? We have enquiries for high temp ASHP.
    One possible application for high temp ASHP for power generation.
    By using Organic Rankine Cycle engine (ORC), even at 85C temp, ORC generates power with an efficiency of 15-17% and you get by-product of hot water at 55-60 deg. C

  18. #68
    Join Date
    May 2008
    Location
    Belgie
    Posts
    13
    Rep Power
    0

    Re: High Temp Heat Pumps

    FACTSHEET 14 / 15: RESTWARMTE AARDAPPELVERWERKENDE INDUSTRIE
    Verdamper 8 bar / 70°C
    Condensor 13 bar / 90°C
    Elektriciteit
    Compressor
    Van
    Blancheur
    Naar
    Blancheur
    Restwarmte
    Retour
    Restwarmte
    Aanvoer
    85°C
    77°C
    80°C
    75°C
    Meerjarenafspraken Energie-efficiency
    14. Hoge-temperatuur
    mechanische warmtepomp
    De aardappelverwerkende industrie kampt over
    het algemeen met een overschot aan restwarmte.
    Een mogelijke toepassing hiervoor is
    het opwaarderen van restwarmte naar een
    hogere temperatuur. Bij een hoge-temperatuur
    warmtepomp wordt de graad van restwarmte
    verhoogd middels een medium. Het werkmiddel
    wordt in een verdamper verdampt met behulp
    van restwarmte. Een compressor verhoogt de
    druk, waarna de warmte op hogere tempera-tuur
    wordt afgegeven in de condensor.
    Werkmiddel
    Conventionele werkmiddelen zoals ammoniak zijn ongeschikt voor warmtepompen op een temperatuur boven 70 °C omdat de druk te hoog wordt: ammoniak heeft bij 90 °C een verdampingsdruk van circa 50 bar. n-Butaan heeft bij 90 °C een acceptabele druk
    van 13 bar, waardoor dit werkmiddel wél geschikt is voor toepassing in hoge-temp warmtepompen. n-Butaan is echter licht
    ontvlambaar; de installatie moet dan ook in een aparte ruimte geplaatst worden.
    Een n-Butaan warmtepomp kan werken met een condensortemperatuur van max. 110 °C.
    Compressor
    De belangrijkste component van de hogetemperatuur warmtepomp is de compressor.
    Deze vergt hoge investeringskosten, verbruikt uiteraard elektriciteit en heeft jaarlijkse
    onderhoudskosten. Hierdoor vallen de netto besparingen lager uit.
    Elektriciteitsverbruik
    Voor een verdamperdruk van 8 bar (70 °C) en een condensordruk van 13 bar (90 °C) komt de COP overeen met 11. Dit verlangt een
    besparing van 0,75 kWh elektriciteit per Nm
    3.

    Bron restwarmte en gebruikers
    Om een redelijke efficiëntie te halen moet de temperatuursverhoging niet al te groot zijn.
    Met restwarmte van 80 °C kan een proces verwarmd worden tot ongeveer 110 °C.
    De belangrijkste gebruikers zijn: blancheurs
    Mogelijke bronnen van restwarmte zijn:
    Afblaas stoomschillers

    Bakdampen

    Rookgassen stoomboiler

    Opmerkingen
    Door de flinke investeringen is een hoge-temp
    warmtepomp meestal alleen rendabel voor grotere vermogens.

    Naast de investering in de installatie om de restwarmte op te waarderen, moet er vaak ook worden geïnvesteerd in de terugwinning van restwarmte.
    Hierdoor vallen de investeringskosten hoog uit.

    De hoge-temperatuur mechanische warmtepompnis een nieuwe toepassing die marktrijp is, maar nog niet is toegepast in de praktijk. Daarom zijn er subsidiemogelijkheden die max. 40 % bedragen van de meerkosten ten opzichte van de gangbare technieken.

    Kengetal len
    COP 11

    Elektriciteitsverbruik 0,75 kWh/ Nm³

    Restwarmte > 75 °C

    Benodigde temperatuur < 90 °C

    Informatiepunt SenterNovem
    (tussen 9:00 - 12:00 uur en 14:00 - 16:00 uur)
    Telefoon 030 239 35 33
    E-mail info@senternovem.nl
    Internet www.senternovem.nl/mja
    REKENVOORBEELD
    Aangezien hoge-temperatuur warmtepompen vooral geschi k t z i jn voor grotere i n stal l a t i es, wordt er gerekend met de warmteterugwinni ng voor b l ancheurs van twee 10 ton l i jnen.
    Er i s voldoende warmte beschi kbaar op 80 °C.
    U i t g a n g s p u n t e n :
    Li jncapac i tei t 2 * 10 ton per uur

    Vermogen b l ancheur 2 * 950 kW

    Temperatuur b l ancheur 80 °C

    O n t w e r p
    Condensor 90 °C / 13 bar

    Verdamper 70 °C / 8 bar

    COP 11

    Benut t ing restwarmte 1.727 kW

    B e s p a r i n g e n
    Aardgas 1 .250.000 Nm³

    El ekt r i c i tei t - 934. 000 kWh

    Net t o bespar ing € 228. 000

    Invest eringskosten € 1.215.000

    Terugverdi ent i jd 5, 3 jaar

    De meer jarenafspraken energie -ef f ic iency (MJA’s) z i j n
    overeenkomsten tussen de min ister ies van Economis che
    Zaken (EZ), Landbouw, Natuur & Voedselkwali tei t (LNV) ,
    Vol kshuisves t ing, Ruimtel i jke Ordening & Mi l ieubeheer
    (VROM) , bedr i jven en inst e l l ingen ove r het e f fect ieve r en
    e f f iciënt e r inzet ten van ene rgie.
    Publ i c a t i enummer : 2MJAF0732 augustus 2007

    n-Butaan als 2de trap ziet er wel goed uit.

  19. #69
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: High Temp Heat Pumps

    A bit bigger than the OP asked for but many of you may find this interesting...

    http://www.star-ref.co.uk/star/image...ian%20Army.pdf
    http://www.star-ref.co.uk/star/image...20Neatpump.pdf

    Smaller CO2 option - chilling and heating in one unit...

    http://www.star-ref.co.uk/star/image...0Envitherm.pdf

Page 2 of 2 FirstFirst 12

Similar Threads

  1. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  2. Heat pumps a bonus for House buyers?
    By mick2me in forum Heat Pumps
    Replies: 21
    Last Post: 14-11-2006, 01:27 PM
  3. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  4. Heat Pumps
    By US Iceman in forum Industrial
    Replies: 11
    Last Post: 14-04-2006, 07:29 PM
  5. R406a for high temp heat pump
    By Lc_shi in forum Refrigerants
    Replies: 1
    Last Post: 14-10-2005, 09:08 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •