Thread: Copper gaskets

  1. #1
    Join Date
    Dec 2008
    Location
    West Yorkshire
    Posts
    63
    Rep Power
    16

    Copper gaskets



    When using brass to brass flare type fittings I have always used a copper (shim) gasket but it seems others are not, due to the possibility of the shim becoming displaced in the fitting. I've looked into this but can't come up with anything definitive. Some of the components provided on compressor units such as HP/LP switches with flexible lines c/w brass couplings aren't fitted with them either.
    Anyone else had this?
    Last edited by sparkatan; 11-03-2020 at 11:02 AM. Reason: wrongly spelt



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Copper gaskets

    FSW still stock them - Flare Gasket

    Code B123 - 1/4"
    Code B124 - 5/16"
    Code B125 - 3/8"

    Etc. (Taken from the FSW catalogue)

    If required, I used to flare the end of a piece of pipe and then cut the flare off.

  3. #3
    Join Date
    Dec 2008
    Location
    West Yorkshire
    Posts
    63
    Rep Power
    16

    Re: Copper gaskets

    Thanks Frank but that's not quite what i'm asking. I've always used shims either 'home made' or purchased but recently I am coming across a lot of instances where they're not being used. The question is whether they are actually needed between two brass surfaces?

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Copper gaskets

    Can't say that I've come across many instances of this, but then again, my line of work didn't bring me into much contact with other peoples install work.

    As old school, I always used copper gaskets between brass/brass joints.

    Looking through the Climate Centre catalogue, I can see some brass fitting pictures shown without the copper gasket and some with

  5. #5
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Copper gaskets

    Always used to use copper flare rings good practice, some people probably don’t use them because they have not been supplied with the kit!

  6. #6
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Copper gaskets

    Carrier 30GX HXC oil pumps were brass to brass fittings with no copper gaskets from factory but many had the copper gaskets fitted when new oil pumps fitted.
    Gibbo

  7. #7
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Copper gaskets

    I always used the copper flare gaskets when fitting brass-brass or brass-steel.

    My take on it is that they didn't start manufacturing them just because some people may like to use them

    2 tricks to make them stay in place:

    -Dab them in a little bit of oil and stick them on the tip of the male fitting and they should stick pretty good and not be dislodged or move out of position.

    -Drop them into the female fitting and use another fitting to tighten and seat the gasket before mounting in the final position.
    -Cheers-

    Tycho

  8. #8
    Join Date
    Dec 2008
    Location
    West Yorkshire
    Posts
    63
    Rep Power
    16

    Re: Copper gaskets

    All very interesting opinions but is there anywhere I can find a definitive answer to this?

  9. #9
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Copper gaskets

    If in doubt use them

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Copper gaskets

    Copper is soft metal while steel and brass are hard, any tiny misalignment might cause scratches and gas leeks are inevitable.
    When copper is pressed between two hard metals' it get their surface shape and seal the connection.

    There are also chemicals such as Nylog which do a good seal.

  11. #11
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Copper gaskets

    The manufacturers of refrigeration brass flare fittings supply copper gaskets inside the box of fittings as the gasket is a requirement to get a gas tight seal when brass to brass or steel to brass fittings are used . When purchasing a few fittings at the wholesalers such as a flare connector etc the copper gaskets should be supplied as part of the fitting . It should not be necessary to purchase these gaskets separately .
    Often the trade counter staff are not aware that there are gaskets in the box of connectors and the gaskets are simply discarded when all of the fittings in the box have been sold . Suppliers like Bailey Gill always supply these gaskets in a small bag in with the fittings, so always ask for them , they are part of the brass fitting not a seperate part.
    The Danfoss flare / solder adaptors come with copper gaskets which have a short piece of tube with the flare gasket ring which positions the gasket to hold it in place
    Last edited by Glenn Moore; 14-03-2020 at 12:02 AM.