    KKT Chiller cBoxX180, R410 A 3 Ph 400 v,77kw



    Hello ,
    Any one help me in kkt chiller 77 kw using in beverage plant ,,with four Danfoss compressors ,,,The two new compressors have been replaced filter core while 24 kg gas charged in system ,,after fifteen days the system LP tripping while low pressure reached on 100 psi lower set point and machine stop,,on that time observation discharge pressure 410 reduce 350 and suction pressure 135 reduce 90 psi bother reduce run time ,,electronic expansion valve Siemens using there,,pressure are not constant both suction and discharge
    Attached Images Attached Images



  2. #2
    Join Date
    Apr 2018
    Location
    TURKEY
    Posts
    17
    Rep Power
    0

    Re: KKT Chiller cBoxX180, R410 A 3 Ph 400 v,77kw

    Might be a problem on the condenser fan regulation. This happens on cold ambient? system runs with air cooled condenser?

  3. #3
    Join Date
    Jun 2017
    Location
    Norway
    Posts
    32
    Rep Power
    0

    Re: KKT Chiller cBoxX180, R410 A 3 Ph 400 v,77kw

    Do you have a leak? What is the subcooling and superheat?

  4. #4
    Join Date
    Nov 2009
    Location
    riyadh(k.s.a)
    Posts
    14
    Rep Power
    0

    Re: KKT Chiller cBoxX180, R410 A 3 Ph 400 v,77kw

    yes its running two air cool condensers fan,,,as well as expansion device ,,siemens ,MVL661.20-2.5

  5. #5
    Join Date
    Nov 2009
    Location
    riyadh(k.s.a)
    Posts
    14
    Rep Power
    0

    Re: KKT Chiller cBoxX180, R410 A 3 Ph 400 v,77kw

    there is no leakage,,,super heat 5.1Kkkt1.jpg

  6. #6
    Join Date
    Apr 2018
    Location
    TURKEY
    Posts
    17
    Rep Power
    0

    Re: KKT Chiller cBoxX180, R410 A 3 Ph 400 v,77kw

    Check the EXV % opening state. If the expansion valve goes around %10-20 while you have these trips, you have a low water flow rate. you might need to check if the pumps are running good, or strainers are clean.

    if this only happens on very cold ambient, than you should change the condenser fan kick in-out setpoints. (if you do not have the opportunity to do so, than try to close 1 stage of fan and see what happens. )