    What are the causes of this overload tripped?
    thanks, rosliin.
    shabeer's Avatar
    shabeer Guest
    Re: Overload tripped lesson
    overload relay trips due to eccessive load than the rated load i.e motor consuming current(over load relay which converts heat energy into mechanical force)
    Mar 2005
    u.a.e
    68
    169
    which overload?
    zhangchunfeng's Avatar
    zhangchunfeng Guest
    Hello
    are you ensure your setting is correct? if it is ok ,
    pls check your voltage in the range. or your have a high ambient temperature .
    hope it is helpful to you
    Best Regards
    Neil
    Jun 2006
    alabama
    olp tripped.
    why eccessive load can be happened?
    Mar 2005
    manchester uk
    82
    11
    i find the usual causes of overload tripping are,compressor burnt/siezed, system blocked.
    CHILL out with Manchester United
    11,025
    Quote Originally Posted by rosliin
    olp tripped.
    As an "AC Technician" (your profile) I am surprised at your question, what are your thoughts on the cause of the overload tripping?
    Jun 2005
    California
    394
    Some causes of overload trips of compressors are:
    1. Refrigerant floodback;
    2. Flooded starts;
    3. Slugging;
    4. Overheating; and
    5. Loss of oil.