    Aug 2009
    Manchester
    178
    Toshiba RBC-AMS41E Hard Wired Controller
    Hi all,
    We have a Toshiba RBC-AMS41E Hard wired controller on a stand alone split system which will not allow a Heating or Auto mode. I'm being told it has had this function but suddenly over night has lost it. The controller will only allow cooling and fan mode with the heating option seemingly now disappeared. The controller has been swapped for another but still same thing. Has someone been messing and locked out heating ? Any advise welcome.
    5,668
    Re: Toshiba RBC-AMS41E Hard Wired Controller
    Perhaps someone has been playing about with the function settings. See page 19 here
    Apr 2008
    Southampton, England
    49
    1,023
    Don't quote me but don't they have a small PCB outdoors which has some dip switches on?
    The switches corrode and one of them is to set this cooling only function.
    Definitely is on one make, not Daikin, Mitsi, Fujitsu that I do know. Pretty sure it was Toshiba.
    Cheers,
    Andy.
    Aug 2009
    Manchester
    178
    Sorry for the late update.
    Tayters, you were spot on. I can confirm it is Toshiba which have such a fault. Cheers guys big help.
    Jul 2020
    Ashburn, Virginia, USA
    1
    Hi..i would suggest you to replace it with new technology. RBC-MTSC1 colour smart touch wall mounted controller is a capacitive icon based touchscreen that is very intuitive, easy to use and very simple to install. The smart touch controller uses the same 2 wire format used for our standard controllers and no external power supply is needed to operate the device.
