    vibration / resonating



    Hi, I'm new to this and need some help with what will seem like very basic questions to you guys in regard to plit wall mounted inverter heat pumps.

    The outdoor unit seems relatively quiet but the noise from it is muchy louder inside. Noise seems to be not only transferring through the pipework to the indoor unit but also the house framing seems to be carrying it.

    Everything seems well insulated and fixed etc.

    The noise is okay until the compressor is at it highest load/speed.

    What are the possible causes and solutions and what should I be looking for?

    Hope you will help as I am unable to get much help from my associates. (Its a long story )

    Thanks...Derek



  2. #2
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: vibration / resonating

    Hi
    "Everything seems well insulated and fixed etc."

    Try loosening all fixing points and recheck - If the noise level goes down then tighten each in turn and check at each stage - this may help you to identify the problem.

    Are the pipes resting on anything?

    Do a search for vibration nulling mountings / screws/ bolts.
    Things like this :- http://www.antivibrationmethodsrubbe...html/foot.html

    HTH

    Paula

  3. #3
    derekj's Avatar
    derekj Guest

    Re: vibration / resonating

    Thanks Paula,
    I appreciate you can be bothered to help with things so basic. I will try that. Is noise transfer in liquids different between different refrigerants operating at different pressures? These I am talking about are using R 410.
    Also these units are pre gassed for 5 metres...How much difference does each metre longer or shorter of pipe run make?

    Regards ...Derek

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: vibration / resonating

    The pipe length shouldn't really make a difference, as Paula suggested try each fixing point in turn.

    It could be that when the compressor is fully loaded, max speed, then a harmonic is being set up somewhere and being transmitted along the pipework into the structure. With the cover off, beware electrics !!!, and the unit running try pressing each bit of pipe with something like a screwdriver (hot pipes will burn your fingers ) to see if the vibration stops.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Vibration Analysis
    By nui in forum Tools and Calculators
    Replies: 8
    Last Post: 11-01-2007, 11:48 PM
  2. Vibration in refrigerant piping
    By US Iceman in forum Technical Discussions
    Replies: 5
    Last Post: 01-05-2006, 11:53 PM
  3. Screw compressor vibration
    By jpumarada in forum Industrial Compressors
    Replies: 14
    Last Post: 26-04-2006, 01:43 PM
  4. Liquid Line's Vibration
    By JERRYCOOL in forum Industrial
    Replies: 20
    Last Post: 21-03-2006, 01:49 AM
  5. Refrigerator Vibration And Backflow
    By GHCGY in forum Trouble Shooting
    Replies: 2
    Last Post: 27-10-2005, 09:41 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •