29-02-2020, 10:18 AM #1
climaventa chiller unit high pressure alarm
hello
I have problem with my ac chiller with my hardware board Same as photo my controller is W3000 controller..
my problem is i have alarm code 211 and 212 is high pressure in circuit 1 and 2,every things in my unit is ok and i check my high pressure is ok and change it by new but still alarm is appear and i connot run compressor.
we I try to change compete hardware board by new no alarm coming because is new board.SO COULD any one help my to to delete this alarm i have now 10 PCB board with same alarm..!!
i have user psassoword is 1234
assitance is 9990
manfactor is 0000009982
also i need super user password ??? can any one give me ???
-
29-02-2020, 10:20 AM #2
Re: climaventa chiller unit high pressure alarm
-
29-02-2020, 10:36 AM #3
Re: climaventa chiller unit high pressure alarm
Have you reset the trip on the High Pressure switch?
-
29-02-2020, 01:18 PM #4
-
29-02-2020, 03:54 PM #5
Re: climaventa chiller unit high pressure alarm
Have you a photo of hp switches
-
29-02-2020, 07:08 PM #6
Re: climaventa chiller unit high pressure alarm
Try the following.
10 ALARMSPress the ALARM key once to enter the “alarms menu” and view the alarm message along with its code.If there is more than one alarm, scroll the menu using the “Up” and “Down” keys.To reset the alarm, press the ALARM key again and HOLD IT DOWN until “No alarm active” is displayed.If the message does not appear it means that one or more alarm conditions are still active.Press any other key to exit from this menu.
Good Luck GrizzlyDespite the High Cost of Living it still remains Popular!
-
01-03-2020, 03:08 PM #7
Re: climaventa chiller unit high pressure alarm
When i tried to press alarm key for 3 second the alarm of high pressure is disappeared but is coming agine after few second.
Every time i have same alarm I just change the complete PCB hardware and every things working good thats means I dont have any problem in my pressure switch.
Around 5 years Im changing around 10 PCB when i have same alarm because i dont have another choose..
-
01-03-2020, 03:14 PM #8
Re: climaventa chiller unit high pressure alarm
Even When I tried to make pay pass for high pressure switch by installed wire jumber but still the alarm appeared..
-
01-03-2020, 07:39 PM #9
Re: climaventa chiller unit high pressure alarm
Is there a second high pressure switch on the circuit that you are missing? Is the motor thermistor in series with this alarm or any other switch?
Mostly found in the southern part of this green and pleasant land.
-
01-03-2020, 11:35 PM #10
Re: climaventa chiller unit high pressure alarm
Like al said you could have a hp transducer and a Manual reset hp switch it’s not uncommon on some makes of chillers
-
03-03-2020, 08:21 AM #11
Re: climaventa chiller unit high pressure alarm
-
03-03-2020, 10:00 AM #12
Re: climaventa chiller unit high pressure alarm
Are the pressure transducers 2 wire or 3 wire?
-
03-03-2020, 03:08 PM #13
Re: climaventa chiller unit high pressure alarm
Press the black button in the middle of the switch that’s the reset
-
04-03-2020, 05:57 AM #14
-
04-03-2020, 05:58 AM #15
-
04-03-2020, 07:37 AM #16
Re: climaventa chiller unit high pressure alarm
After pressing the black button you must do what Grizzly said
-
04-03-2020, 09:26 AM #17
Re: climaventa chiller unit high pressure alarm
Do you have continuity through the 2 wires from the sensor?
Disconnect it from the pcb and measure for continuity with a multimeter - even when pressing the reset button.
-
04-03-2020, 09:59 AM #18
-
04-03-2020, 10:02 AM #19
Re: climaventa chiller unit high pressure alarm
All HP switch has been changed by new but still same alarm . I tried today to change complete board PCB and alram is going .. thats mean I dont have any problem in my unit only in PCB and now I have 11 PCB with same alarm .
I think there is some software problem may be
-
04-03-2020, 10:05 AM #20
-
04-03-2020, 12:37 PM #21
Re: climaventa chiller unit high pressure alarm
If you link out the HP switch does your chiller run?
-
04-03-2020, 01:28 PM #22
Re: climaventa chiller unit high pressure alarm
Have you got a photo of the wiring diagram
-
04-03-2020, 06:23 PM #23
-
04-03-2020, 06:24 PM #24
-
05-03-2020, 10:33 AM #25
Re: climaventa chiller unit high pressure alarm
https://www.manualslib.com/manual/49...page=30#manual
Here is the manual, there is a description of the board and connections. Also check the factory settings - at what pressures HP is etc.
Maybe it will help.
[Google translator]
-
05-03-2020, 04:38 PM #26
Re: climaventa chiller unit high pressure alarm
What is the Alarm Number on the display?
-
06-03-2020, 09:30 AM #27
-
08-03-2020, 07:15 AM #28
Re: climaventa chiller unit high pressure alarm
Did any body know how to connect my Pc to this PCB
Which software can I use ?? DCC16C95-256C-4B51-9E0E-B415E126B87B.jpg
-
13-07-2020, 05:40 AM #29
Re: climaventa chiller unit high pressure alarm
Any update
-
15-07-2020, 01:13 AM #30
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: climaventa chiller unit high pressure alarm
If you have continuity whole time on control circuit related to that alarm, you should take that board to electronic repair shop and tell them to check digital inlet which is related to that alarm. Probably optocoupler issue!
If there is no problem with related digital inlet than it is software issue and you should contact dealer of these units!Last edited by nike123; 15-07-2020 at 01:20 AM.
-
15-07-2020, 01:18 AM #31
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
15-07-2020, 03:38 PM #32
Re: climaventa chiller unit high pressure alarm
Had a similar problem turned out to be the battery module which feeds the alarm relays if memory serves me right. Caused by low battery voltage but for some reason gives up hp fault.
GibboLast edited by Gibbo; 15-07-2020 at 03:42 PM.
-
13-08-2020, 09:40 AM #33
-
18-08-2020, 05:20 AM #34
Re: climaventa chiller unit high pressure alarm
did any boady have any idea how to connect my PCB of chiller to my PC ? there is any software can i use it?
-
23-08-2020, 10:02 AM #35
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: climaventa chiller unit high pressure alarm
https://www.carel.com/programming-to...KK/10191/54942
https://www.carel.com/product/c-suite
But you probably dont have acess to change programing off these PCO-s since Climavenata is making its own software for PCO and it is protected.
Your best bet is to contact manufacturer.
By my expirience, they will never admit that their software is faulty and you will be bounced around like some stupid monkey folowing their instructions. But, maybe you will be lucky monkey!
I usualy install μchiller2 SE in that case, if it is possible.Last edited by nike123; 23-08-2020 at 10:27 AM.
-
26-08-2020, 02:21 PM #36
Re: climaventa chiller unit high pressure alarm
Are you sure that High pressure alarm comes from HP switch but not HP sensor?