    Chiller Carrier



    Can someone tell me from where I can obtain the technical manual/electrical for this chiller - 30GH030 - 710AEE and the overhaul manual for it's compressor 06E 6275 RA 610A EE.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51
    Take a look at www.global.carrier.com on their technical section

  3. #3
    Join Date
    Dec 2001
    Location
    Malta
    Posts
    18
    Rep Power
    0
    Frank

    Thanks

    I have a problem with this chiller - I need to see if the compressor windings are burnt or a mechanical failure.

    The compressor system is without an overload and the probability is that there are no internal thermistors .

    Winding, is part winding and too ground I have 3 mega ohms while between each winding A & B I do have 0.13 Mega ohm. the problem is, a burn-out ,mechanical failure or a contaminated area within the oil etc,at least before I will dismantle the compressor.

    My experiance is on Trane centrifugal units although I worked on reciprocating compressors a few years ago.

    Any comments

    victor

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51
    Victor

    You should never mega a motor between windings! but should always mega between winding and earth. If you have a reading of 0.5mohm and above then, according to british regs the resistance to earth is acceptable, however, all of the people I know work to a resistance of at least 1m ohm. Anything less and we usually condem the motor. With a resistance of 3m ohm to earth your motor would appear to be OK as far as the winding insulation is concerned and more investigation is required to locate the problem.

  5. #5
    Join Date
    Dec 2001
    Location
    Malta
    Posts
    18
    Rep Power
    0
    Frank

    Thank you

    The 0.13 M ohm is between:see attachment

    point 8 & 2
    point 7 & 1
    Point 3 & 9

    3.5 Mohm is between any point too earth

    Any comments are welcomed

    Victor


    Victor

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Question

    Victor - I'm not sure where to find the attachment. Can you point me in the right direction?

  7. #7
    Join Date
    Dec 2001
    Location
    Malta
    Posts
    18
    Rep Power
    0
    Frank

    I cannot find a way to attach the document.

    thank you

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Exclamation

    Maybe one of the Moderators can show us 'new starters' how to attach documents

  9. #9
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26
    In your "post reply" section , scroll down and you will see the ATTACH FILE option, beneath OPTIONS.
    Select the file from your hard drive.

    Browsing this through thread, I think there is a bit of confusion. The information I believe is contained within the Carrier pages, not within an attached file on this forum.

    I visited the Carrier site, and found no technical info.....

    Regards

  10. #10
    Join Date
    Dec 2001
    Location
    Canada
    Age
    69
    Posts
    53
    Rep Power
    23
    What are the symtoms of the compressor failure? Is running at all? Is it noisy when it runs? Is it tripping the breaker or blowing fuses? Can you read the current draw when it does?

    If it's a part winding start, is there a delay between the contactors pulling in? Is it about 1 second?

    To check the motor windings use an ohm meter on a low scale.
    From my experience, depending on the voltage, you should end up reading the same across all motor windings. Here, the readings would be about one ohm or less across each of them.

  11. #11
    Join Date
    Feb 2005
    Location
    UK
    Age
    44
    Posts
    13
    Rep Power
    0

    Talking Re: Chiller Carrier

    How have you tested the motor? did u test it with all the windings connected to the contactor? you should disconnect all the cables at the compressor before testing it for burn out. you should use your multi meter for testing between the windings - expect 0.8-2 ohms (ish) for between each part wind section (3 terminals each) you should then check between each terminal and a ground (cpc/earth) point, as before anything less than say 1M ohm (tho i would be worried if it was 2M or less). you could also test the contactor for continuity, disconnect the cabes to the compressor and allow the contactor to be activated by the controller and check that the correct voltage is present. Also did you check the incoming voltage? have yo lost a phase? or is there one slightly down not allowin the motor to spin?!?!

  12. #12
    Join Date
    Nov 2004
    Location
    uk
    Age
    77
    Posts
    61
    Rep Power
    20

    Wink Re: Chiller Carrier

    The 06E is carriers "bread and butter" recip..it should present you with few problems..personally I use a megger at 500 volts to earth to check the motor terminals....if that is ok you can get a rough balance check(though not as accurate as a purpose made balance tester) by using the same megger set to ohmsX1 which should be about 5 volts....check each half of the partwind motor between each of its three terminals....they would normally give you a reading that is around 0.8 or 0.9 and would be balanced....if there are service valves fitted to the compressor then you can use the backseat port to evacuate the gas....then remove the square plate from the end of the oil pump...inside is a cup and spring underneath which is a small cam plate held by two dissimilar sized allen screws..you should be able to turn the compressor over using an allen key in the larger of the screw heads....as this compressor has no side access plates it is possible to get a "rough" idea of the condition of the small and big ends by removing the heads ...turning over the compressor and giving a sharp push on the top of each piston as it is on its downward stroke...if there is major wear you will feel it ..if you have further problems I am happy to assist....best of luck...I have stripped and repaired a few hundred of these over the years....they are a simple compressor but need inverting to get to the big ends...crank removal etc...

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 02:42 AM
  2. carrier chiller fault codes
    By al in forum Air Conditioning
    Replies: 7
    Last Post: 20-07-2009, 10:10 PM
  3. Trane & Carrier Chiller Data
    By mustafa in forum Air Conditioning
    Replies: 8
    Last Post: 03-05-2009, 04:10 PM
  4. Carrier chiller oil migration
    By lowtech in forum Industrial
    Replies: 5
    Last Post: 30-04-2006, 04:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •