Clivet chiller... Wsat-xsc3 110.4
Good day Engineers,
Please, I'm having problems with a clivet Chiller with the alarm EE1018.
I tried to reset but the unit is not reset.
Please can anyone help with information on how to resolve this problem..
Thanks..
-
06-10-2019, 08:11 PM #2
Re: Clivet chiller... Wsat-xsc3 110.4
its side ventilation over load circuit no 1 have you checked the overload
-
07-10-2019, 02:22 AM #3
Re: Clivet chiller... Wsat-xsc3 110.4
Thanks Mr martinw58.
The Condenser fan motors are Variable Speed as I can't find any overload.
-
07-10-2019, 09:47 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Clivet chiller... Wsat-xsc3 110.4
https://www.airview.nl/resources/upl...04/INSTAL1.pdf
Here is the installation manual.
EE1018-Source side protection-Source side ventilation overload protection-Circuit 1
Find electrical diagram and check all what is in circuit connecting to digital input 119
119-Source inverter protectionLast edited by nike123; 07-10-2019 at 09:51 AM.
-
07-10-2019, 02:18 PM #5
Re: Clivet chiller... Wsat-xsc3 110.4
Thank you Mr Nike123, I will do just that when I go to the site by next week