    Clivet chiller... Wsat-xsc3 110.4



    Good day Engineers,
    Please, I'm having problems with a clivet Chiller with the alarm EE1018.
    I tried to reset but the unit is not reset.

    Please can anyone help with information on how to resolve this problem..

    Thanks..



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Clivet chiller... Wsat-xsc3 110.4

    its side ventilation over load circuit no 1 have you checked the overload

  3. #3
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: Clivet chiller... Wsat-xsc3 110.4

    Thanks Mr martinw58.
    The Condenser fan motors are Variable Speed as I can't find any overload.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Clivet chiller... Wsat-xsc3 110.4

    https://www.airview.nl/resources/upl...04/INSTAL1.pdf

    Here is the installation manual.

    EE1018-Source side protection-Source side ventilation overload protection-Circuit 1

    Find electrical diagram and check all what is in circuit connecting to digital input 119

    119-Source inverter protection
    Last edited by nike123; 07-10-2019 at 09:51 AM.

  5. #5
    Join Date
    Jun 2016
    Location
    Nigeria
    Posts
    64
    Rep Power
    8

    Re: Clivet chiller... Wsat-xsc3 110.4

    Thank you Mr Nike123, I will do just that when I go to the site by next week