    E4 code on AUX air conditioner



    Hi lads
    i am having problem with e4 code on a new aux split system. i do not know who installed it , it does not look like a pro job. i want to change the evap sensor but feel it might be the board. any idea how to fix it?



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: E4 code on AUX air conditioner

    Yes call an engineer

    Good luck

  3. #3
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: E4 code on AUX air conditioner

    Both coil and room sensors are okay.
    Please do not send smart remark .

  4. #4
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: E4 code on AUX air conditioner

    Quote Originally Posted by sork View Post
    Both coil and room sensors are okay.
    Please do not send smart remark .


    Good luck.,....,
    Last edited by r.bartlett; 14-10-2019 at 07:25 AM.

  5. #5
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: E4 code on AUX air conditioner

    It seems to be a Drainage system failure

    au x.jpg

  6. #6
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: E4 code on AUX air conditioner

    Thanks Narkom .

  7. #7
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: E4 code on AUX air conditioner

    、E4 by chigo states: Check whether the winding resistance andoperation current of the compressor are normal.2、Check whether the high and low pressure is normalwhen the unit is running.3、Check (whether the coil pipe sensor is normal)whether the contact of the inserter on the circuitboard is well, the coil pipe temperature sensor isfixed, the evaporation of the indoor unit is well,the key is to check the evaporator temperaturedetected by the coil pipe temperature sensor hasreached the cooling or heating temperature.4、Check whether the surface of the condenser is toodirty, it should be cleaned when it is too dirty.5、Check whether the capacitance of the outdoor motorand the fan is damaged, it should be replaced whenit is damaged.6、If the above items are normal, the electric controlboard should be replaced.