    Dear Sirs,
    Is it normal to measure current on Motor grounding cable IF no can this cause unbalance current.
    Please be informed we have two motor one by inverter and the other one by soft-starter and they have the same problem (unbalance current)
    grounding system TNC
    looking forward to read from you
    Thank you
    Sep 2009
    Iran
    66
    672
    1
    Re: unbalance current
    Unbalanceing current can be from .
    Unequal of voltage
    Unequal of ohm's in Electromotor
    Leak or damaging wiring in electromotor
    Loose wire in connection box or wiring system
    Test electromotore with megger and leak of that
    Don't worry for
    2 of 3 percent unbalancing with equal voltage .
    Feb 2012
    libya
    41
    94
    13
    thank you mbc
    the current unbalance more than 10% and nothing from the above
    Sep 2009
    Iran
    66
    672
    1
    Also if you have broken conduction on ROTORS Your current always move and come down and goes up .
    Feb 2012
    libya
    41
    94
    13
    this is an ammonia plant with two stage each stage with separate electrical panel but both of them supply from same transformer the current unbalance occur only in one stage and we notice this unbalance for all the motor compressors and pumps
    Oct 2009
    77
    243
    Check your voltages phase to phase not phase to earth or neutral sounds like could be low voltage on supply voltage
    Feb 2012
    libya
    41
    94
    13
    The source voltage phase to phase as following:
    V1=380.1 v
    V2=383.2 v
    V3=377.9 v
    The load voltage phase to phase as following:
    V1=372.1 v
    V2=380.3 v
    V3=374.3 v
    The source power feeds the load through 6 single core 300mm2
    Somerset
    69
    4,700
    47
    Erm!
    Sorry for being silly!
    But What exactly is your problem with the plant?
    Only that's not 10% error
    Does your plant not operate properly or are you just worried about what you are seeing\/
    Aug 2014
    75
    508
    The way invertors are grounded can cause many problems . Also the type of invertor can cause current issues. The size of the earth bonding cable and its route from the motor to the invertor etc all can cause problems . Is the invertor sensing a current problem and alarming or is this just an observation
    What are the current readings at the motor terminals as the safeties in the invertor and the soft starter should detect any problem and log any errorp
    Feb 2012
    libya
    41
    94
    13
    The two screw compressors driven by the same invertor type SINAMICS G130 one of them has current unbalance and the other no
    please see attached motors readings
    cp1 Percentage Imbalance: 9.3% (invertor )
    cp2 Percentage Imbalance: 14.1% (Soft starter)
    cp3 Percentage Imbalance: 2.3% (invertor)
    cp4 Percentage Imbalance: 2.2% (Soft starter)
    cp1 and cp2 MP, also the pump connected to this panel has current unbalance
    cp3 and cp4 LP
    Split Croatia
    57
    6,151
    36
    Inverter powered motors and soft starters always have current on motor grounding cable because of inverter filtering circuit.
    What I would suggest is call energy distribution company specialist to check distribution panel and cables since unbalance is common factor on one distribution panel.
    Feb 2012
    libya
    41
    94
    13
    we are still troubleshooting and i am sure you will help me gentlemen and now are thinking of the electro- magnetic fields which generated by single core cables but we are wondering why only this panel, the other one ok and they are from the same transformer the same main distribution panel
    Thank you