    Mitsi Fault



    Hi,

    Breify looked at system not cooling today, its a twin split with a PUH-5... outdoor on R22.

    The filters on the 2 cassettes were blocked so washed them out but was getting a P8 (abnormal discharge temp?) fault on the remote.

    Put my gauges on the suction schreader, had a head pressure of around 7.5bar, and ran the sytem in test mode. Compressor ran, air off condenser was just ambient, liquid line was sweating, suction was around 1.5 bar. So first thoughts were that it was undercharged. On closing of manifold gauge after adding some vapour, the pressure remained at around 7.5bar again, with the comp still running.

    Could there be a blockage somewhere? The suction service valve is after the 4-way reversing valve if that helps?



  2. #2
    Join Date
    May 2006
    Location
    Leicestershire
    Age
    58
    Posts
    28
    Rep Power
    0

    Re: Mitsi Fault

    Hi slim
    we have had reversing valves stick half giving the fault you have idicated,i suggest you switch the unit off a lightly tap the body of the valve or energise the coil a couple of times to see if it seats properly.

  3. #3
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Mitsi Fault

    Thanks for the help,

    I tried tapping the valve whilst it was running but not while it wasnt. When you say energise the coil I presume you mean ask it to heat, should there be 240v on the coil when it asks for heat mode?

  4. #4
    Join Date
    May 2006
    Location
    Leicestershire
    Age
    58
    Posts
    28
    Rep Power
    0

    Thumbs up Re: Mitsi Fault

    Quote Originally Posted by Slim R410a
    Thanks for the help,

    I tried tapping the valve whilst it was running but not while it wasnt. When you say energise the coil I presume you mean ask it to heat, should there be 240v on the coil when it asks for heat mode?
    When your next passing a fridge wholesaler pop in and by a coil magnet,they fit most sol valves and of course you dont need to keep running to the outdoor unit to see if its gone on heating mode.Simple idea and a useful tool for engineers i think its called a fridgemag?

  5. #5
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Mitsi Fault

    Quote Originally Posted by Slim R410a
    Thanks for the help,

    I tried tapping the valve whilst it was running but not while it wasnt. When you say energise the coil I presume you mean ask it to heat, should there be 240v on the coil when it asks for heat mode?
    Some units energise the coil on cooling.

Similar Threads

  1. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  2. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM
  3. Mitsi Fault
    By richelli in forum Trouble Shooting
    Replies: 2
    Last Post: 27-03-2006, 07:20 PM
  4. Mitsi HEAVY
    By Latte in forum Air Conditioning
    Replies: 4
    Last Post: 27-01-2006, 02:21 PM
  5. Mitsi Problems
    By Latte in forum Air Conditioning
    Replies: 9
    Last Post: 12-02-2005, 07:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •