    Copeland ZRD-81 noise issue during modulation



    Hi,
    I have a problem with compressor ZRD81. AC unit is equipped with one compressor and during PWM modulation, when pressure LP and HP are almost same - appears strange noise (check link below):

    https://drive.google.com/file/d/18Nh...ew?usp=sharing

    Any ideas what is going on?

    Thanks



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Copeland ZRD-81 noise issue during modulation

    Can't get the audio to work, maybe there is not enough pressure differential to hold the scrolls together as designed at low load. The digital scrolls (not sure if that what you have) do growl a bit when unloading and loading.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Copeland ZRD-81 noise issue during modulation

    Quote Originally Posted by Partykus View Post
    when pressure LP and HP are the same
    When the system is off and pressures are equalised then this statement could be true but I struggle to imagine a running system with equal pressures?

  4. #4
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Copeland ZRD-81 noise issue during modulation

    compressor running the wrong way ?

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Copeland ZRD-81 noise issue during modulation

    Some times just before pressure equalized, scroll is turning backwards .
    To avoid it' a NRV should be installed on the discharge line.

  6. #6
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Copeland ZRD-81 noise issue during modulation

    Hi
    Most scrolls has this chek valve

  7. #7
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Copeland ZRD-81 noise issue during modulation

    sounds like gas pulsing through a valve

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Copeland ZRD-81 noise issue during modulation

    Probably mechanically damaged compressor!
    Check this thread on another forum:
    https://hvac-talk.com/vbb/showthread.php?2194688-Copeland-scroll-rattling-noise-every-10-15-seconds