    air cooler uneven distribution check



    Hi sirs
    One expert told me the method to check if the refrigerant is distributed well or not for a fin tube air cooler. The procedure as below:
    Vacuum the air cooler and charge liquid refrigerant into it and watch the frost situation and confirm if the distributor is good or not.
    I can't make sure if it's correct. Have you known this method?

    best regards
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    May 2006
    Location
    Leicestershire
    Age
    58
    Posts
    28
    Rep Power
    0

    Re: air cooler uneven distribution check

    Hi Lc shi

    The best way to check a multi port distributer is too leave the refrigeration system running but turn off the evaporator fan motors,remove the evaps end covers and look for the frost line on each curcuit of the evap. This will produce a frost line on all coils except the curcuit which is blocked,if all of the runs frost then there is no distributor problem it may be the TEV setting.

    P.S don't leave it running for too long as you may have liquid refrigerant going back to the compressor.

  3. #3
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    807
    Rep Power
    20

    Re: air cooler uneven distribution check

    I think you're right.
    thanks

    regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: air cooler uneven distribution check

    Hi LC,

    Why are you checking the refrigerant distribution visually?

    If the coil circuiting is done properly and the distributor is selected correctly, these problems are non-existent.

    The biggest problem I am aware of is the need for proper coil circuiting. If multiple distributors are used to control part load operation, you might want to ensure the coil circuit will provide a completely active coil surface.

    Otherwise, you can loose control of the dehumidification of the air stream if the coil is only partially active.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: air cooler uneven distribution check

    We let it run normally and just one bend before it enters the main suction header (oppositeside of tehj suction header), you measure if all these last return bends have the same temperature.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,086
    Rep Power
    25

    Re: air cooler uneven distribution check

    I agree with Peter. But in the case of split coil distribution such as I see with the gentle air unit coolers that use low velocities out of both sides such as you find in meat preparation areas, I have struggled with even distribution dilemmas because I now have possibly unequal air flows.

    Thus, you can have an unequal distribution that is caused by unequal air flow, or heat load. Always keep this in mind. This could apply to an A-coil in your home air conditioner, and also a horizontal refrigeration freezer coil in a reach in freezer.

    Vacuum the air cooler and charge liquid refrigerant into it and watch the frost situation and confirm if the distributor is good or not.
    Lc, this is a terrible idea for simple reasons. You only have one chance to look at it and your are done with your analysis. That's the first one that comes to mind.
    Last edited by Dan; 17-06-2006 at 12:50 AM.

Similar Threads

  1. Air conditioning maintenance procedure
    By Andy T in forum Air Conditioning
    Replies: 12
    Last Post: 27-05-2006, 06:57 PM
  2. Thermo-syphon Oil Cooler
    By B.B. in forum Industrial
    Replies: 5
    Last Post: 31-10-2005, 02:25 PM
  3. Double check needed
    By Latte in forum Trouble Shooting
    Replies: 14
    Last Post: 11-08-2004, 12:46 PM
  4. Compressor Check for locked rotor voltage
    By shogun7 in forum Trouble Shooting
    Replies: 0
    Last Post: 04-04-2004, 12:44 AM
  5. freezer is now a cooler
    By superheat in forum Commercial
    Replies: 20
    Last Post: 18-03-2003, 01:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •