Results 1 to 50 of 54

Hybrid View

  1. #1
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: compact screw oil carry over

    Hi 12embo
    you wrote: Hi RANGER1
    1. Evaporator is a flooded flake ice drum


    if your system is a flooded system, I can't see any device for an oil return from it.
    So the oil missing in the oil separator is probably the oil drained from the ice machine + the oil mixed with refrigerant in the surge drum.

  2. #2
    Join Date
    Apr 2016
    Location
    Iran
    Posts
    42
    Rep Power
    0

    Re: compact screw oil carry over

    Quote Originally Posted by cricri View Post
    Hi 12embo
    you wrote: Hi RANGER1
    1. Evaporator is a flooded flake ice drum


    if your system is a flooded system, I can't see any device for an oil return from it.
    So the oil missing in the oil separator is probably the oil drained from the ice machine + the oil mixed with refrigerant in the surge drum.
    Sorry you are right. The system is not flooded. It is direct expansion with throttling valve.