    Refrigerant compressed air dryer



    Dear Colleagues

    In a refrigerant air dryer R22, I would like to replace the High Pressure Switch, setting in 28Bar (CUT OUT), with a thermostat and I would like to know at what temperature must be set (CUT OUT).

    Thanks a lot.

    Best Regards



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Refrigerant compressed air dryer

    Set the same temperature as the original pressure setting was at.

    Same switch, different dial.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: Refrigerant compressed air dryer

    Hi kaskiris
    If it is a HP safety I would not replace it with a thermostat.
    Regards
    Paul
    Born to fish, forced to work

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Refrigerant compressed air dryer

    why replace a high pressure safety switch with a thermostat

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Refrigerant compressed air dryer

    Quote Originally Posted by martinw58 View Post
    why replace a high pressure safety switch with a thermostat
    Probably because it has failed and he doesn't have a spare available on the island.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Refrigerant compressed air dryer

    This sounds a very strange idea and potentially dangerous . For a thermostat to work, 1) it’s bulb would need to be fitted in one particular position on the system ,2) the bulb would need to be insulated from air movement etc , 3) the thermal lag of the thermostat would need to be taken into consideration.
    The thermostat setting would be approx 70 deg C . provided the bulb was fitted to the correct position in the system.
    In theory an HP pressure switch will work anywhere on the high side of the system from the discharge pipe through to the liquid line. A thermostat though would only work correctly in one area only .
    Perhaps Kashmiris can tell us specifically where he would fit the thermostat bulb as this would need to be correct for correct functionality of the stat to take place.

  7. #7
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Refrigerant compressed air dryer

    Is Cyprus really that isolated you can’t get parts overnight, or in a few days?

    http://etapol.com/index.php/thermostats-controls

  8. #8
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Refrigerant compressed air dryer

    dose Cyprus come under f gas regs with regards to working on old R22 equipment

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Refrigerant compressed air dryer

    Is the OP going to reply or are we wasting our time here