    Please help me to know how many KW we can get more by adding economizer to our Ammonia Plant which consist of:
    2 MYCOM screw compressors type 200VLD-M @ sst-3 and sdt38
    2 MYCOM screw compressors type 200VLD-L @ sst-11 and sdt38
  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39
    Re: upgrade ammonia plant
    Quote Originally Posted by mre212 View Post
    MRE212, As requested
    Mycom 200VLD M (recommended L port with & without economiser)
    -3 sst without economiser 1063 kw 231 absorbed power
    With economiser 1125 kw 235
    Mycom 200VLD L (recommended M port with economiser).
    -11sst without economiser. 772kw 222kw absorbed
    With economiser. 843kw
    3550 rpm 936kw absorbed 269kw
    economiser 1021kw absorbed 273kw.
    Suggest contact Mycom or representative company, as you are asking to much.
  3. #3
    Join Date
    Feb 2012
    Location
    libya
    Age
    41
    Posts
    94
    Rep Power
    13
    Thank you RANGER for your reply and answer
    two compressors from the mentioned above with VSD how much this will adding the capacity?
    2 SC NH3 @ -11/+38 for 2 PHE MEG -8/-4°C one to feed Blast cooler, Cold store and the other one to feed Ice bank how much kw +1/+6°C as iced water and if i add another PHE for the ice bank can i get more kw for the same volume
  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39
    See my previous updated post