Indoor Unit Not cooling
Recently we have installed then20 HP City multi VRF system and among 8 indoor units 5 are working fine and on rest of the 3 units are not working means on 3 units, we are not getting cooling.i think expansion valve are not opening. so is there any setting to open the expansion valve of the indoor unit. waiting for your positive response.
-
10-06-2019, 08:35 PM #2
Re: Indoor Unit Not cooling
are you sure the units are wired and addressed correctly
-
10-06-2019, 08:36 PM #3
Re: Indoor Unit Not cooling
is the gas charge correct
-
11-06-2019, 03:55 AM #4
-
16-07-2019, 08:27 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Indoor Unit Not cooling
How did you checked gas charge?
Do you hear clicking noise when energizing indoor units that are not opening valves?Last edited by nike123; 16-07-2019 at 08:33 PM.
-
06-12-2019, 05:06 AM #6
Re: Indoor Unit Not cooling
The air filter might be clogged. because clogging air cannot flow through properly which greatly reduces the cooling capacity of the air conditioning.
Last edited by geminair; 06-12-2019 at 09:43 AM.
-
06-12-2019, 10:34 AM #7
Re: Indoor Unit Not cooling
Sound like a wiring problem to me.
Check the wires again to make sure it is correct.
3 units not working is not likely to a manufacture problem.