    Daikin RZQSG71L3V1B No power to indoor



    Hey folks, just wondering if anyone has come across anything similar on a Daikin RZQSG71L3V1B? I’ve an indoor unit that has no power, it’s fed off the outdoor which does have power. I assume it’s either a blown fuse or a faulty PCB? I should add that I had the green LED flashing but no lights on any of H1P to 7. Going back tomorrow with a tall ladder to properly reach and investigate.
    Last edited by eire1; 11-12-2019 at 08:17 PM. Reason: Spelling



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Daikin RZQSG71L3V1B No power to indoor

    there are two fuses in the out door unit

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin RZQSG71L3V1B No power to indoor

    Check the High Float switch on the condensate pump. Some installers put the live or neutral through this switch to stop the unit if the pump fails.

  4. #4
    Join Date
    Mar 2011
    Location
    Dublin
    Age
    36
    Posts
    55
    Rep Power
    14

    Re: Daikin RZQSG71L3V1B No power to indoor

    Thanks guys. Found F1 on the outdoor blown. Mini Lime was fine, all indoor connections OK. I found a loose neutral for a pump for outdoor drip trays. I can only assume that this races and blew it. Ran fine for 60 mins once repaired.