Results 1 to 4 of 4
-
07-06-2019, 03:58 PM #1
Carrier Vector 1800 turns off AL41
Hello
I have a problem with a Carrier Vector 1800.
At outside temperatures above 30 ° C , the engine will run for 15 minutes, then the engine will be out of AL 41.
Just before she turns off the high pressure rises above 25 bar.
Capacitor was cleaned.
Thank you
-
14-08-2019, 07:27 AM #2
Re: Carrier Vector 1800 turns off AL41
Hello,
you should update the microprocessor Software to the newest (05.16.00).
When its done, you have more options to activate.
In the Configuration Menu, you have the Menu AC Power Settings.
Now you have to activate "High Amb Diesel Offset"
-
16-08-2019, 08:03 PM #3
Re: Carrier Vector 1800 turns off AL41
Fit your gauges and just check that pressure is being reached I had one do that because the truck pulling it had eminox exhaust stacks and it filled the coils up with soot good wash out of it went good as new unit
-
16-08-2019, 11:09 PM #4
Re: Carrier Vector 1800 turns off AL41
Nice to read your knowledgeable input Charlie.
Despite the High Cost of Living it still remains Popular!