    condenser heat rejection



    please for your help i have air cooled condenser but no data please i need to know the cooling capacity of it ?

    thank you



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: condenser heat rejection

    If you could put the make and model details up, we mioght have a better chance of helping you.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    Feb 2012
    Location
    libya
    Age
    41
    Posts
    94
    Rep Power
    13

    Re: condenser heat rejection

    i don't have data. can i calculate The heat rejection of an air cooled condenser from this equation :
    Qrej = U · A · LMTD

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: condenser heat rejection

    Do you have any data on the expansion valve make and model? This might give you a rough guide.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: condenser heat rejection

    Hi
    Please measure the length of pipes and dia of that with how many fine has in one inch and size of fins

    Also nomber of fans with espification of that

  6. #6
    Join Date
    Feb 2012
    Location
    libya
    Age
    41
    Posts
    94
    Rep Power
    13

    Re: condenser heat rejection

    Coil length =2743 mm
    Coil Height =1067 mm
    Number of rows =3
    pipes diameter = 10 mm
    Fins per foot (Alu slit fins) =192