    carel mpxpro
    having an annoying issue with a carel controller, fitted to a cold room with air on and off probes, no defrost probe. I'm trying to set room to control on 70% air on via parameter /4.
    Room will only control on air off probe though, what am i missing?
    Mostly found in the southern part of this green and pleasant land.
  2. #2
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21
    Re: carel mpxpro
    Is the inlet probe working?
    Extract from manual,
    * intake probe Sr error: MPXPRO starts control based on the outlet probe
  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41
    Re: carel mpxpro
    Yes, i've checked each probe is reading, also it would bring up an error on controller.
  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41
    Re: carel mpxpro
    Found the problem, i'd mistakenly set RD2, put this back to zero and virtual probe works!
  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,706
    Rep Power
    46
    Re: carel mpxpro
    its a wise man that can admit to his mistakes.
    And in this case a very helpful one!
    Thanks for the valuable info Al.
    Grizzly
    Despite the High Cost of Living it still remains Popular!
  6. #6
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41
    Re: carel mpxpro
    Thanks Grizz