Results 1 to 12 of 12
    Feb 2010
    Portugal
    47
    4
    Systemair chiller code
    Good: I need help with passwords from a chiller SYSTEMAIR model: AQWL 1604 HSE from 2014 thank you.
    Feb 2017
    77
    4
    Re: Systemair chiller code
    What controller is on the unit?
    Feb 2010
    Portugal
    47
    4
    the controller is a carel pco thanks
    Feb 2017
    77
    4
    Quote Originally Posted by danyyelmorg View Post
    in my passwords it just says the default password is "1234"
    Thats all i have unfortunately, what issue are you having with the unit?
    Feb 2010
    Portugal
    47
    4
    I need the maintenance password to set the temperature probe for the superheat of the electronic expansion valve. This code did not give access thanks
    Feb 2017
    77
    4
    have you got a photo of the controller?
    Feb 2010
    Portugal
    47
    4
    controller photo
    This is the only photo I have.
    Feb 2017
    77
    4
    controller photo
    have you got the evd interface? its been a while since i needed to use my interface but im sure you can set the superheat ect on that?
    Feb 2017
    77
    4
    If you have the evd interface the 2 passwords you require is:
    22 = Service level password
    66 = Manufacturer password
    Hopefully they will get you where you want/need to be
    71
    10,740
    If you download the instructions for the eev they will give you the above codes.
    Feb 2017
    77
    4
    Did you manage to sort the issue with them codes?
    Aug 2017
    United Kingdom
    5
    Default CAREL passwords will always be "1234" or "0000" - anything else and they've been configured by the OEM/Panel Builder in order to stop engineers interrogating set points without consulting them!
    As above poster mentioned, you can use the EVD display (EVDIS00EN0) to adjust set points such as super heat.