    Chiller Problem Daikin EWAD350E-SL



    Hi ,

    I am having problem with running chiller Daikin model -EWAD350E-SL

    The chiller cannot run in auto mode .

    In manual model the chiller reach 10 % power and go in error +C1Cmp1 OffSlidePosSen.

    The chiller is used Mcquay screw compressor .

    The error cannot be reset and pop up again .



  2. #2
    Join Date
    Feb 2017
    Location
    UK
    Posts
    117
    Rep Power
    9

    Re: Chiller Problem Daikin EWAD350E-SL

    Hello,

    Your fault code "+C1Cmp1 OffSlidePosSen"

    Trigger: Sensor shorted or open
    Action Taken: Rapid stop compressor
    Reset: This alarm can be cleared manually via the keypad, but only if the sensor
    is back in range.

    Hope that gives you some more information

  3. #3
    Join Date
    Feb 2010
    Location
    Bulgaria
    Age
    38
    Posts
    36
    Rep Power
    0

    Re: Chiller Problem Daikin EWAD350E-SL

    I try to clear this error many times but it show it again

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Chiller Problem Daikin EWAD350E-SL

    Have you checked the sensor?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Feb 2017
    Location
    UK
    Posts
    117
    Rep Power
    9

    Re: Chiller Problem Daikin EWAD350E-SL

    Quote Originally Posted by yanev22 View Post
    I try to clear this error many times but it show it again
    It will only stay clear once the sensor is back in range, have you tested it?

    expected range is 4 to 20mA.

  6. #6
    Join Date
    Feb 2010
    Location
    Bulgaria
    Age
    38
    Posts
    36
    Rep Power
    0

    Re: Chiller Problem Daikin EWAD350E-SL

    How can be tested ?

    Anyone have electric diagram for this model chiller ?