    Feb 2010
    Bulgaria
    36
    Chiller Problem Daikin EWAD350E-SL
    Hi ,
    I am having problem with running chiller Daikin model -EWAD350E-SL
    The chiller cannot run in auto mode .
    In manual model the chiller reach 10 % power and go in error +C1Cmp1 OffSlidePosSen.
    The chiller is used Mcquay screw compressor .
    The error cannot be reset and pop up again .
    Feb 2017
    112
    9
    Re: Chiller Problem Daikin EWAD350E-SL
    Hello,
    Your fault code "+C1Cmp1 OffSlidePosSen"
    Trigger: Sensor shorted or open
    Action Taken: Rapid stop compressor
    Reset: This alarm can be cleared manually via the keypad, but only if the sensor
    is back in range.
    Hope that gives you some more information
    Feb 2010
    Bulgaria
    36
    I try to clear this error many times but it show it again
    11,025
    Have you checked the sensor?
    Feb 2017
    112
    9
    Quote Originally Posted by yanev22 View Post
    It will only stay clear once the sensor is back in range, have you tested it?
    expected range is 4 to 20mA.
    Feb 2010
    Bulgaria
    36
    How can be tested ?
    Anyone have electric diagram for this model chiller ?